All PowerTag products use ZigBee Green Power which is not supported by LM ZigBee implementation.
Posts: 1758
Threads: 6
Joined: Jul 2015
Reputation:
115
Only way to add them is through a PASx00 server so you can read them over Modbus TCP
Posts: 7649
Threads: 41
Joined: Jun 2015
Reputation:
441
Get any other sensor that uses standard ZigBee, not ZigBee Green Power.
Posts: 7649
Threads: 41
Joined: Jun 2015
Reputation:
441
We have tested PowerTags before but it was not a 100% stable solution so it was decided not to support it.
Posts: 7649
Threads: 41
Joined: Jun 2015
Reputation:
441
LM ZigBee gateway can possibly communicate with Green Power devices but from our experience most Green Power devices are meant to be used only with their original gateways.
When PowerTag sends data to the gateway it awaits a confirmation message to be sent back to it. The timing window for this confirmation is very short, so it's nearly impossible to implement this via a router. The only more or less stable third-party solution for PowerTags requires a specific gateway with a custom firmware.
Posts: 334
Threads: 74
Joined: Jun 2017
Reputation:
6
Hi,
For Schneider please use PAS400, PAS600 devices for Schneider power tag. PAS device has LAN, Info from powertags you receive to LM over Modbus IP. Not sure it will works with any other ZGP than Schneider.
Alex