Hi, I'm having some troubles trying to read float32 values from modbus, setting the profile as below, read value on KNX is always 0. When I try to read using "read test" as 32float it seems to work...
"mapping": [
{"name": "SETPOINT_csp1_[R/W]",
"bus_datatype": "float32",
"type": "register",
"datatype": "float32",
"address": 900,
"read_offset": 0,
"read_count": 2,
"writable": true,
"value_delta": 0.1,
"value_multiplier": 1,
"units": "ºC"
Threads: 30
Delete the read_offset and read_count. Drop a screenshot of correct settings from Read test.
Threads: 30
you are missing the read_swap n
Threads: 30
Do you have any errors under Modbus-Error log?
Try setting both data types to uint32. What value is ready then?
TCP implementation on certain Modbus devices is very buggy. Usually only a limited amount of connections can be created and it takes some time for the device to detect disconnect and free up a used connection. Sometimes this can be fixed by enabling the "Persistent connection" mode.
At the moment value delta minimum is 0.2. This had to be done because a lot of installations are overloaded by not setting the delta properly.
In you read test screenshot you are using TCP connection. Have you tried enabling Persistent connection mode? Try rebooting your Modbus device as well.
See my previous post about adding read_delay to the profile for RS485 devices.
Might be some edge case. Just add read_delay and see if it helps. Another option to try is using a lower baud rate if possible.