This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Control KODI
#1
Good afternoon,

Has anyone tried to control KODI through homelynk?
I would like to know if it is possible and how it can be done in such a case.


Thank you so much,
Reply
#2
(18.04.2017, 15:32)Superchango Wrote: Good afternoon,

Has anyone tried to control KODI through homelynk?
I would like to know if it is possible and how it can be done in such a case.


Thank you so much,

Hello, yes i use it but my code is very basic and needs some beautification Sad

the library
Code:
function kodiHandler(iServer,iPort,sendPort)
 -- first call
 if not ready then
   require('socket')
   
   lastdatareceived = nil
   ready = true
 end
 
 -- client connected
 if connected then
   while true do
     char, err = client:receive(1)
     -- error while receiving, closed socket
     if err == 'closed' then
         connected = false
       sleep(1)
       break
     end
       
     if char ~= nil then
       lastdatareceived = os.time()
       warningclosed = true
       warningfailed = true
       warningerrors = true
       warningtimeou = true
       
                table.insert(buffer, char)
       tmpbuf = table.concat(buffer)
       if ( json.pdecode(tmpbuf) ) then
         data = tmpbuf
         parse(data)
         buffer = {}
       end
     else
       now = os.time()
       deltatime = now - lastdatareceived
     end
       
     -- receive incoming send requests
         msg, ip, port = sendServer:receivefrom()
            if msg then
       -- send command
       --log("send: "..msg)
       client:send(msg)
            end
     
     --[[ clear not complete buffer
     if deltatime > 10 and #buffer > 0 then
       log( #buffer )
       buffer = {}
       lastdatareceived = os.time()
     end
     -]]
   end
   
   -- first call or previously disconnected
 else
   -- close previous connection when disconnected
   if client then
     client:close()
     client = nil
   end
   if sendServer then
     sendServer:close()
     sendServer = nil
   end
   
   -- create tcp client
   client = socket.tcp()
   client:settimeout(5)
   connected, err = client:connect(iServer, iPort)
   
   -- connect ok, reset buffer
   if connected then
     lastdatareceived = os.time()
     warningclosed = true
     warningfailed = true
     warningerrors = true
     warningtimeou = true
     --log('[KODI-client] connection ok: '..iServer)
     buffer = {}
     
     -- create udp server to receive incoming send requests
            if not sendServer then
              sendServer = socket.udp()
              sendServer:setsockname('*', sendPort)
              sendServer:settimeout(0.1)
            end
     
     sleep(5)
     
     -- send initial command
     --client:send( '{"jsonrpc": "2.0", "method": "Player.PlayPause", "params": { "playerid": 0 }, "id": 1}' )
     
   
     -- error while connecting,
   else
            --log(err)
     if warningfailed then log('[KODI-client] connection failed (conn): '.. err) end
     warningfailed = false
     sleep(5)
   end
 end
 
 -- incoming command parser
 function parse(data)
   -- log other info, not mapped, if useful
   --log("data received: "..data)
   --log(json.pdecode(data))
 end
end

the resident script
Code:
require('user.nit_kodi')
require('json')

kodiHandler("192.168.x.x","9090","18007")

-- callback from handler
-- tv recording play
function tvrecPlay()
 log("test1")
end
-- tv recording - pause or stop
function tvrecStop()
  log("test2")
end
in another script u can use for example:
Code:
udpsend( '{ "jsonrpc": "2.0", "id": 1, "method": "Application.SetVolume", "params": { "volume": 50 } }', "18007" )
Reply
#3
Thanks I will put with it to see if I am able to perform a control of my HTPC with KODI
Reply
#4
Hi,

My "solution" is even more basic.

I installed an USB IR Flirc receiver on my Kodi box and programmed it with a Samsung remote control. I then use a Global Caché IR transmitter that is controlled through simple TCP commands.

In my visualisation I have programmed a "universal" remote control with which I can control my cable decoder, AVR, Kodi and TV.

Attached Files Thumbnail(s)
   
Reply
#5
One more simple KODI control solution:


Code:
require('socket.http')
socket.http.TIMEOUT = 5

-- play ---------------------------------------------------------------------------------------------
data1 = socket.http.request('http://192.168.1.79:8080/jsonrpc?request={ "jsonrpc": "2.0", "method": "Input.ExecuteAction", "params": { "action": "play" }, "id": 1 }')

-- pause --------------------------------------------------------------------------------------------
data1 = socket.http.request('http://192.168.1.79:8080/jsonrpc?request={ "jsonrpc": "2.0", "method": "Input.ExecuteAction", "params": { "action": "pause" }, "id": 1 }, "id": 1 }')

-- down ---------------------------------------------------------------------------------------------
data1 = socket.http.request('http://192.168.1.79:8080/jsonrpc?request={"jsonrpc": "2.0", "method": "Input.Down", "id": 1}')

-- up -----------------------------------------------------------------------------------------------
data1 = socket.http.request('http://192.168.1.79:8080/jsonrpc?request={"jsonrpc": "2.0", "method": "Input.Up", "id": 1}')

-- right --------------------------------------------------------------------------------------------
data1 = socket.http.request('http://192.168.1.79:8080/jsonrpc?request={"jsonrpc": "2.0", "method": "Input.Right", "id": 1}')

-- left ---------------------------------------------------------------------------------------------
data1 = socket.http.request('http://192.168.1.79:8080/jsonrpc?request={"jsonrpc": "2.0", "method": "Input.Left", "id": 1}')

-- home ---------------------------------------------------------------------------------------------
data1 = socket.http.request('http://192.168.1.79:8080/jsonrpc?request={"jsonrpc": "2.0", "method": "Input.Home", "id": 1}')

-- select -------------------------------------------------------------------------------------------
data1 = socket.http.request('http://192.168.1.79:8080/jsonrpc?request={"jsonrpc": "2.0", "method": "Input.Select", "id": 1}')
Reply
#6
(19.04.2017, 14:23)leonidas Wrote: One more simple KODI control solution:


Code:
require('socket.http')
socket.http.TIMEOUT = 5

-- play ---------------------------------------------------------------------------------------------
data1 = socket.http.request('http://192.168.1.79:8080/jsonrpc?request={ "jsonrpc": "2.0", "method": "Input.ExecuteAction", "params": { "action": "play" }, "id": 1 }')

-- pause --------------------------------------------------------------------------------------------
data1 = socket.http.request('http://192.168.1.79:8080/jsonrpc?request={ "jsonrpc": "2.0", "method": "Input.ExecuteAction", "params": { "action": "pause" }, "id": 1 }, "id": 1 }')

-- down ---------------------------------------------------------------------------------------------
data1 = socket.http.request('http://192.168.1.79:8080/jsonrpc?request={"jsonrpc": "2.0", "method": "Input.Down", "id": 1}')

-- up -----------------------------------------------------------------------------------------------
data1 = socket.http.request('http://192.168.1.79:8080/jsonrpc?request={"jsonrpc": "2.0", "method": "Input.Up", "id": 1}')

-- right --------------------------------------------------------------------------------------------
data1 = socket.http.request('http://192.168.1.79:8080/jsonrpc?request={"jsonrpc": "2.0", "method": "Input.Right", "id": 1}')

-- left ---------------------------------------------------------------------------------------------
data1 = socket.http.request('http://192.168.1.79:8080/jsonrpc?request={"jsonrpc": "2.0", "method": "Input.Left", "id": 1}')

-- home ---------------------------------------------------------------------------------------------
data1 = socket.http.request('http://192.168.1.79:8080/jsonrpc?request={"jsonrpc": "2.0", "method": "Input.Home", "id": 1}')

-- select -------------------------------------------------------------------------------------------
data1 = socket.http.request('http://192.168.1.79:8080/jsonrpc?request={"jsonrpc": "2.0", "method": "Input.Select", "id": 1}')

With this solution you have no incoming data, so you can't turn off your lights when a movie starts for example.
Reply
#7
(19.04.2017, 14:28)gjniewenhuijse Wrote: With this solution you have no incoming data, so you can't turn off your lights when a movie starts for example.

Yes, but it's better than using Global Cache.
Reply
#8
(20.04.2017, 07:25)leonidas Wrote: Yes, but it's better than using Global Cache.

yes, you're right.
Reply
#9
(19.04.2017, 12:04)baggins Wrote: Hi,

My "solution" is even more basic.

I installed an USB IR Flirc receiver on my Kodi box and programmed it with a Samsung remote control. I then use a Global Caché IR transmitter that is controlled through simple TCP commands.

In my visualisation I have programmed a "universal" remote control with which I can control my cable decoder, AVR, Kodi and TV.

Hi Baggins,

Since I see the "Telenet" symbol on your visualisation I assume we live in the same country. 
To avoid re-inventing hot water, here Could you share some tcp commands you use to control your cable decoder + give some insight on how you built the visualisation shown in the screenshot of your post?

kr,

B.
Reply
#10
(11.09.2017, 21:02)Bart Wrote:
(19.04.2017, 12:04)baggins Wrote: Hi,

My "solution" is even more basic.

I installed an USB IR Flirc receiver on my Kodi box and programmed it with a Samsung remote control. I then use a Global Caché IR transmitter that is controlled through simple TCP commands.

In my visualisation I have programmed a "universal" remote control with which I can control my cable decoder, AVR, Kodi and TV.

Hi Baggins,

Since I see the "Telenet" symbol on your visualisation I assume we live in the same country. 
To avoid re-inventing hot water, here Could you share some tcp commands you use to control your cable decoder + give some insight on how you built the visualisation shown in the screenshot of your post?

kr,

B.

Hi,

As I've stated, I use a Global Caché (it actually is the Basalte version) transmitter attached to the Telenet Digicorder.
Here is the script I use to control the Digicorder:

Code:
--[[
   Command: Command for execution by controller of Global Cache. To transmit IR command Command=sendir. See full list in GLobal Cache manual.
   Modul: The module containing the appropriate IR port (e.g. for iTach=1
   NumDev: Number of port in the module starting with 1.
   Id: Id number of the command in range 0 – 65535
   Freq: IR channel frequency in Hz, from 20000 – 500000
   Repeat: on 0 – repeat the command up to 65535 times or while the command transmit is terminated
   Offset: Time period to repeat the telegram in the next transmissions (Repeat<>1), 1 – 255
   P0,…,Pn: String sequence defining impulse sequence in IR telegram
   ^: Symbol defining the end of command string, OD (Hex)

--]]


local socket = require("socket")

function send_Digicorder(command)
 log('send_Digicorder called; command ' .. command)
tcp = assert(socket.tcp())
tcp:settimeout(0.5)

 Device = '192.168.0.26'                                                      
 Header =  "sendir,1:2,1,38000,1,1,"
                                           
 connected, err = tcp:connect(Device, '4998')                                                    
--print (connected)
--print (err)
Digicorder = {}

Digicorder["BACK"] =             "11,12,12,24,12,12,23,24,12,12,23,24,23,25,11,12,23,12,12,12,11,13,11,24,23,3362\r"
Digicorder["CHANNEL DOWN"] =     "11,12,11,25,11,13,23,25,11,13,23,25,22,25,11,13,23,25,23,12,11,25,23,3359\r"
Digicorder["CHANNEL UP"] =       "11,12,11,25,11,13,22,25,11,13,23,25,23,25,11,13,22,25,23,25,23,25,11,3348\r"
Digicorder["CLEAR"] =            "11,13,11,25,11,13,23,25,11,13,23,25,23,25,11,13,23,13,11,13,11,25,11,13,23,3364\r"
Digicorder["COMMUNICATION"] =    "12,12,11,25,11,13,22,25,11,12,23,25,23,24,12,13,11,12,23,13,11,12,12,24,23,3362\r"
Digicorder["CURSOR DOWN"] =      "11,13,11,25,11,12,23,25,12,12,23,25,23,25,11,13,23,13,11,24,23,25,23,3360\r"
Digicorder["CURSOR ENTER"] =     "11,12,11,25,11,13,22,25,11,13,23,25,23,25,11,13,22,13,11,25,23,13,11,25,11,3348\r"
Digicorder["CURSOR LEFT"] =      "11,13,11,25,11,12,23,25,11,12,23,25,23,25,11,13,23,13,11,25,11,12,11,13,23,3360\r"                                                        
Digicorder["CURSOR RIGHT"] =     "11,13,11,25,11,12,23,25,11,12,23,25,23,25,11,13,23,13,11,25,11,12,23,25,11,3351\r"
Digicorder["CURSOR UP"] =        "11,13,11,25,11,13,23,25,11,13,23,24,23,25,11,12,23,25,22,13,11,13,11,25,11,3349\r"
Digicorder["DIGIT 0"] =          "11,13,11,25,11,12,23,25,11,12,23,25,23,25,11,13,11,12,23,25,23,25,23,3365\r"
Digicorder["DIGIT 1"] =          "11,13,11,25,11,13,23,25,11,13,23,25,22,25,11,13,11,12,12,13,11,13,11,12,23,25,11,3347\r"
Digicorder["DIGIT 2"] =          "11,13,11,25,11,13,23,25,11,13,23,25,22,25,11,13,11,12,11,13,11,13,23,25,23,3360\r"
Digicorder["DIGIT 3"] =          "11,13,11,25,11,13,23,25,11,13,22,25,23,25,11,13,11,13,11,13,11,13,22,13,11,25,11,3348\r"
Digicorder["DIGIT 4"] =          "11,13,11,25,11,13,23,25,11,13,22,25,23,25,11,13,11,13,11,12,23,25,11,12,23,3360\r"
Digicorder["DIGIT 5"] =          "11,12,11,25,11,13,22,25,11,12,23,25,23,24,11,13,11,13,11,12,23,24,23,25,11,3327\r"
Digicorder["DIGIT 6"] =          "11,13,11,25,11,13,23,25,11,13,23,25,22,25,11,13,11,13,11,12,23,12,11,25,23,3362\r"
Digicorder["DIGIT 7"] =          "11,13,11,25,11,13,23,25,11,13,23,25,22,25,11,13,11,13,11,12,23,12,11,13,11,25,11,3353\r"
Digicorder["DIGIT 8"] =          "11,13,11,25,11,13,23,25,11,13,23,25,22,25,11,13,11,13,23,25,11,13,11,12,23,3359\r"
Digicorder["DIGIT 9"] =          "11,12,11,25,11,13,23,25,11,13,23,25,23,24,11,13,11,13,23,25,11,13,23,25,11,3345\r"
Digicorder["ENTER"] =            "11,25,11,13,23,25,11,13,11,13,22,25,22,25,11,13,23,25,11,13,22,25,23,3363\r"
Digicorder["EXIT"] =             "11,12,11,25,11,13,23,25,11,13,23,25,23,25,11,13,23,12,11,13,11,25,23,25,11,3350\r"
Digicorder["EXTRA"] =            "12,13,11,25,11,12,23,25,11,12,23,25,22,25,11,13,11,12,23,12,12,12,11,13,11,24,12,3351\r"
Digicorder["FORWARD"] =          "11,13,11,25,11,13,23,25,11,13,23,25,23,25,23,25,11,13,11,13,11,13,11,13,23,3360\r"
Digicorder["FUNCTION BLUE"] =    "11,12,12,24,12,12,23,24,12,13,23,24,23,24,23,25,23,24,11,13,23,24,11,3351\r"
Digicorder["FUNCTION GREEN"] =   "12,12,11,25,11,12,23,25,11,12,23,25,23,25,23,24,12,12,23,12,11,13,11,25,11,3350\r"
Digicorder["FUNCTION RED"] =     "11,13,11,24,12,12,23,24,12,12,23,24,23,25,23,24,12,13,23,12,11,25,23,3358\r"
Digicorder["FUNCTION YELLOW"] =  "12,12,12,25,11,13,22,25,11,13,22,25,23,24,23,25,22,25,11,12,12,12,23,3364\r"
Digicorder["GUIDE"] =            "11,13,11,25,11,12,23,25,11,12,23,25,23,25,11,13,11,13,23,12,11,25,23,24,12,3356\r"
Digicorder["HELP"] =             "11,13,11,24,12,12,23,24,12,12,23,24,23,25,11,12,23,25,11,12,23,25,23,3359\r"
Digicorder["MENU MAIN"] =        "11,12,12,25,11,13,22,25,11,13,23,25,23,25,11,12,23,25,12,12,11,13,11,13,23,3362\r"
Digicorder["MUTE TOGGLE"] =      "11,13,11,25,11,12,23,25,11,12,23,25,22,25,11,13,23,25,11,13,11,13,23,25,11,3347\r"
Digicorder["PAUSE"] =            "11,13,11,25,11,12,23,25,11,12,23,25,23,25,23,25,11,13,11,13,11,13,23,24,12,3345\r"
Digicorder["PLAY"] =             "11,13,11,25,11,12,23,25,11,12,23,25,23,25,23,25,11,13,23,25,11,13,23,3363\r"
Digicorder["POWER TOGGLE"] =     "11,12,12,24,12,12,23,24,12,12,23,24,23,24,12,12,12,12,23,24,23,12,12,24,12,3349\r"
Digicorder["PREVIOUS CHANNEL"] = "11,13,11,25,11,12,23,25,11,12,23,25,23,25,11,13,23,13,11,12,11,13,11,25,22,3361\r"
Digicorder["RECORD"] =           "11,13,11,24,12,13,23,24,11,13,23,24,23,25,23,25,11,13,11,12,23,25,23,3363\r"
Digicorder["REVERSE"] =          "11,13,11,25,11,13,23,25,11,13,23,25,22,25,11,13,23,13,11,13,12,12,11,13,11,25,11,3352\r"
Digicorder["STOP"]   =           "11,12,11,24,11,12,23,24,11,12,23,24,22,25,22,24,11,12,11,12,22,12,11,24,12,3297\r"
Digicorder["TELETEXT"] =         "11,12,12,24,12,12,23,24,12,12,23,24,23,24,23,25,11,12,23,25,23,24,11,3346\r"
Digicorder["VOLUME DOWN"] =      "11,13,11,24,12,13,23,24,11,13,23,24,23,25,11,12,23,25,23,25,11,13,22,3362\r"
Digicorder["VOLUME UP"] =        "11,13,12,24,11,13,23,24,11,13,23,25,23,25,11,12,23,25,11,12,23,12,11,25,11,3345\r"                                                            

                                                       

   if command == 'OK' then
     command = 'CURSOR ENTER'
   end
    result = tcp:send(Header .. Digicorder[command])  
    --log('Result: ' .. result)
    rec = tcp:receive()
    --log(rec)
    tcp:close()  

                                                                                               
                                                     
end


As far as the visualisation is concerned: Inkscape and GIMP are your friends...
Reply
#11
You can go one step further with Kodi web interface and stream content to your computer from your Kodi system.
Reply