bacnet rs485
Hello, Can you communicate in BACNET with port rs485 on Homelynk or spacelynk?
SORRY FOR MY ENGLISH
BACnet MSTP is not supported.
It is the same thing for logicmachine?
And is it possible to use the Bacnet Client
http://openrb.com/logicmachine-as-bacnet-client/
on spacelynk ?
SE ECO EXPERT
Yes it works, but you will break BTL certification as it is not included in the BTL path.
Make sure to use correct version.
We also don't support it (yet), so questions can only be asked here.
(28.06.2017, 15:58)Erwin van der Zwart Wrote: Yes it works, but you will break BTL certification as it is not included in the BTL path.
ok, but I don't understand:
- why I break BTL certification ? and i's not the case with LM vs spacelynk ?
- how to install package (there is no install package in system menu of spacelynk)
- what ipk package, do you have a link
SE ECO EXPERT
You break BTL certificate because the client is never been part of the BTL certification path and tests.
When you add it you add BACnet options that where never part of this procedure.
The reason we haven't included it is that it would require a re-certification and thats very expensive..
I don't know if LM is also BTL certified, you have to ask Admin.
ok, understood.
However, you didn't reply to
- do you have link for the package ? I found "genohm-scada-bacnet_20170530_mxs.ipk" and "genohm-scada-bacnet_20170530_imx6.ipk"
Thanks for your precious help.
SE ECO EXPERT
(29.06.2017, 07:14)domotiqa Wrote: ok, understood.
hi
as I know, HL and SL have only imx28 CPU , so you should use this package: "genohm-scada-bacnet_20170530_mxs.ipk"
"- how to install package (there is no install package in system menu of spacelynk)"
I think Erwin could help you
hi
I put the lib, www... in the new firmware. I have now the tab, I will test in a close futur
SE ECO EXPERT
Ok I test and only "analog output" display value....
ANalog input, binay input  don't display value. I tried with script, with same result
what I have:
- analog value
- binary output
What I don't have:
- analog input
- binary input
I discuss with a Trend
I tried with Bacnet explorer and it's ok !
SE ECO EXPERT
Values are indeed not showed in the client explorer tab, but they do answer to a request. (admin can you check this)
require('bacnet')
value = bacnet.readvalue(100, 'binary input', 1)
log(value)
value = bacnet.readvalue(100, 'analog input', 1)
log(value)
(14.07.2017, 09:21)Erwin van der Zwart Wrote: Hi,
require('bacnet')
log(value)
log(value)
SE ECO EXPERT