This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus and Nibe Modbus40
#12
You should set "write multiple" = true.
I don't use the log.set, because of the limit of 20 regs.
Very important to set the polling frequence to 1 sec, and timeout to 3sec when polling without log.set.
Reply


Messages In This Thread
Modbus and Nibe Modbus40 - by eirik - 14.07.2017, 10:34
RE: Modbus and Nibe Modbus40 - by admin - 14.07.2017, 10:42
RE: Modbus and Nibe Modbus40 - by eirik - 14.07.2017, 10:51
RE: Modbus and Nibe Modbus40 - by admin - 14.07.2017, 10:56
RE: Modbus and Nibe Modbus40 - by eirik - 14.07.2017, 11:28
RE: Modbus and Nibe Modbus40 - by admin - 14.07.2017, 11:38
RE: Modbus and Nibe Modbus40 - by merel - 17.07.2017, 15:42
RE: Modbus and Nibe Modbus40 - by eirik - 21.07.2017, 09:14
RE: Modbus and Nibe Modbus40 - by Mrinj - 15.03.2019, 17:42
RE: Modbus and Nibe Modbus40 - by merel - 16.04.2019, 07:28
RE: Modbus and Nibe Modbus40 - by RagingBull - 14.06.2019, 14:52
RE: Modbus and Nibe Modbus40 - by eirik - 15.06.2019, 14:04
RE: Modbus and Nibe Modbus40 - by RagingBull - 20.06.2019, 07:17
RE: Modbus and Nibe Modbus40 - by merel - 21.06.2019, 07:10
RE: Modbus and Nibe Modbus40 - by PassivPluss - 27.06.2019, 17:15
RE: Modbus and Nibe Modbus40 - by merel - 01.07.2019, 06:47
RE: Modbus and Nibe Modbus40 - by PassivPluss - 09.11.2019, 06:43
RE: Modbus and Nibe Modbus40 - by Daniel - 11.11.2019, 09:32
RE: Modbus and Nibe Modbus40 - by admin - 11.11.2019, 09:59

Forum Jump: