Hello, what to do when you have an error in the sreenshot attached.
We init the trend with bad datatype... or sometimes you get a false value and you want to remove only this value ?
-----------
FRANCE SMARTHOME & SMARTBUILDING INTEGRATION
SE ECO EXPERT
Posts: 68
Threads: 3
Joined: Jun 2016
Reputation:
0
Maybe you can update the trend directly in the DB, but not sure how to do this or even if it's possible.
I let admin answer, or maybe Erwin.
Posts: 1764
Threads: 6
Joined: Jul 2015
Reputation:
117
Hi,
Trends are not stored in the normal DB but in RRD files (round-robin database)
Deleting data from this trend data files is not easy to do as there are multiple calculations done on the data (average data points).
As i see on the trend there is almost no data in it yet so i would advice to delete current trend and recreate it on the correct dpt.
BR,
Erwin
Posts: 264
Threads: 39
Joined: Feb 2016
Reputation:
1
(24.08.2017, 20:56)Erwin van der Zwart Wrote: Hi,
Trends are not stored in the normal DB but in RRD files (round-robin database)
Deleting data from this trend data files is not easy to do as there are multiple calculations done on the data (average data points).
As i see on the trend there is almost no data in it yet so i would advice to delete current trend and recreate it on the correct dpt.
BR,
Erwin
yes I did it.
I found also that in backup we can modify it !
I was speaking about this problem, because in other project, sometimes you have bad modbus communication, then wrong value, then Trend with terrible Axis resolution !
-----------