RE: Modbus profiles examples - Daniel - 15.04.2025

Is the GND connected between devices?


RE: Modbus profiles examples - nhemtman - 28.04.2025

(15.04.2025, 12:48)Daniel Wrote: Is the GND connected between devices?

Hi,


The Modbus master device does not have a GND connection (see attachment ECP202EXP.PNG).


RE: Modbus profiles examples - Daniel - 28.04.2025

Check all suggestions from this thread
https://forum.logicmachine.net/showthread.php?tid=5946&pid=38562#pid38562


RE: Modbus profiles examples - admin - 28.04.2025

It's possible that INP-GND or PROBE-G can be used. Power down the unit and check resistance between INP-GND and PROBE-G. Most likely inputs are not isolated and resistance should be close to 0. Then check the resistance between RS485-A and INP-GND / RS485-B and INP-GND. Report the values that you get.


RE: Modbus profiles examples - Ranjeet - 22.05.2025

(21.11.2024, 13:37)admin Wrote: If you need a profile for ABB B23 112-10M then we can help with creating it.

Hii sir Sorry for this threat. I need profile for ABB B23 112-10 please help me to create this


RE: Modbus profiles examples - admin - 23.05.2025

See the attached profile. It's not tested so some modifications might be needed. Use Modbus profiler app for this: https://forum.logicmachine.net/showthread.php?tid=5911


RE: Modbus profiles examples - ALEJANDRO - 25.02.2026

Good afternoon,

I'm having some trouble with the Modbus Profiler because I'm not getting Modbus data from some CIRCUTOR counters that I have connected to Logic Machine 5 via gateways. I've attached photos of the counter models, gateway, mapping, variables, profiles, etc.
https://docs.circutor.com/docs/M362B01-01.pdf
https://docs.circutor.com/docs/M239B01-01.pdf



As you can see, both the Modbus TCP gateway and the counter are from the CIRCUTOR brand. I created a profile to extract the data from the counter for active power and total energy measured by the counter, but for some reason it doesn't write to objects 1/2/4. I don't know if you see anything strange in the profile creation in the Modbus Profiler. Thank you very much.


RE: Modbus profiles examples - Daniel - 25.02.2026

Use Read test to check if you have communication and if your profile settings are correct.


RE: Modbus profiles examples - ALEJANDRO - 26.02.2026

What is Read Test?

LM app?


RE: Modbus profiles examples - AEK - 26.02.2026

(26.02.2026, 07:17)ALEJANDRO Wrote: What is Read Test?

LM app?

it is a button at bottom of Modbus tab


RE: Modbus profiles examples - ALEJANDRO - 04.03.2026

ohhh, ok, I use to work with spanish interface, I didn't realize