Modbus-knx tp filter - BuildingAutomation - 02.03.2018

Hi everyone!

I mapped some Modbus device registers to some knx adresses, but i don't want the LM5 to send the values to the knx bus (TP). I have tried using the filtering in "knx connection" and exclude the range I don't want to send too, on the knx bus, (24/*/* and 25/*/*). But when I hit the ok button, the filter get's cleared.

Any ideas?

B,R 

BA


RE: Modbus-knx tp filter - admin - 03.03.2018

Disable "Write to bus" in Modbus mapping


RE: Modbus-knx tp filter - Erwin van der Zwart - 03.03.2018

Just use virtual objects (32 to 63)

BR,

Erwin


RE: Modbus-knx tp filter - BuildingAutomation - 05.03.2018

I have the "write to bus" unchecked.

I would prefer to have the group addresses in the knx range, so that I can manage them in ETS.

B,R

BA


RE: Modbus-knx tp filter - admin - 05.03.2018

Are you sure it's going to KNX bus? If you are monitoring with ETS with LM or KNX router you will see telegrams even when "Write to bus" is disabled, because this setting only affects KNX/TP but not KNX/IP.


RE: Modbus-knx tp filter - BuildingAutomation - 05.03.2018

I have only connected with ip, I'll test with USB next time I'm at the site. 

BR,

BA