Movement sensor with lux condition - Bobby - 11.06.2018

Hi!

I have a movement sensor who controls the lightning.
but i want a condition that says if the lightning level is above 300 lux, the lightning will not turn on.
does anybody have a good script for this?


RE: Movement sensor with lux condition - Jayce - 12.06.2018

This will work fine. Paste this inside the sensor switch object, change those group addresses which are marked 'x/x/x'.


Code:
value = event.getvalue() -- Value of current object
LUX = grp.getvalue('x/x/x') -- change this to group address of your LUX sensor

if (value == false) then -- turns off the light
     grp.write('x/x/x', false) -- Change this to your light object group address
end

if (value == true  and LUX < 300) then -- condition to turn the light on when level of LUX is under 300.
     grp.write('x/x/x', true) -- Also change this to your light group address object
end

Also, if you are by any chance using Auro by Basalte, you don't need script at all, everything can be set-up in your ETS project.