plc - balatis - 13.06.2018

hi 
i try to connect with a plc tm 2412 schneider , the network is modbus tcp. i create a json with only one variable . first i tested the variable from spacelyn with an other device( linkbox) and working  after i testing the plc with with linkbox and it working but the plc with spacelynk can not connect . the json is "mapping": [
{ "name": "Input 1", "bus_datatype": "float16", "type": "inputregister", "address": 1, "value_multiplier": 0.001, "units": "V"}
  ]

}



any help acceptable with appreciation.


RE: plc - admin - 13.06.2018

Anything in Error logs? Try reading with a script and log the read result/error.


RE: plc - balatis - 13.06.2018

(13.06.2018, 07:06)admin Wrote: Anything in Error logs? Try reading with a script and log the read result/error.

in the error log nothing is clear ,i do not now if is correct the json ...  how is possible to read with script ?
thanks


RE: plc - Daniel - 13.06.2018

Hi
Stupid question, but did you map object to your registry?
BR


RE: plc - balatis - 13.06.2018

(13.06.2018, 12:05)Ντάνιελ. Wrote: Γεια
Stupid ερώτηση, αλλά εσείς χάρτη αντικειμένων στο ληξιαρχείο σας;
BR

ΗΙ .
yes i can to shape the map in the plc now for test i use only one variable


RE: plc - Daniel - 13.06.2018

I mean in LM not PLC


RE: plc - balatis - 13.06.2018

(13.06.2018, 12:33)Daniel. Wrote: I mean in LM not PLC

i have a value but is not realy
with same setings the spacelynk working with an intesis box and plc working with intesis box


RE: plc - Daniel - 13.06.2018

Then you have connection and you read a value. This means your conversion is wrong. By looking on the SoMachine This value is not float only int16 and you should not be using multiplayer.


RE: plc - balatis - 13.06.2018

(13.06.2018, 13:06)Daniel. Wrote: Then you have connection and you read a value. This means your conversion is wrong. By looking on the SoMachine This value is not float only int16 and you should not be usingis 
is fault the json? the somachine has integer..... is possible to help me with json?


RE: plc - Daniel - 13.06.2018

{ "name": "Input 1", "bus_datatype": "int16", "type": "inputregister", "address": 1}

Try this.


RE: plc - balatis - 13.06.2018

(13.06.2018, 13:41)Daniel. Wrote: { "name": "Input 1", "bus_datatype": "int16", "type": "inputregister", "address": 1}

Try this.

now in the error log i have this     tes (TCP 192.168.1.10:502) read failed: Illegal function


RE: plc - admin - 13.06.2018

Try changing type to register