Strange behavior LM5 Lite Power (FW 20170620) - gtsamis - 31.08.2018

On 27/08 I had a short (5-10 sec) power failure on a customer's house but after that everything seemed to be working fine.
On 30/08 I tried to login to LM's admin interface (/scada-main) but got a "404 Not Found" error, the same error appeared on the system config page (/flashsys). 
Visualization, trend logs and schedulers seemed fine, bus side, event and scheduled scripts also seemed to be working fine so i did a reboot on the device and after that everything seemed ok... except that all records (logs, alerts etc) was updated till 27/08.
Today I did try to update the firmware to 2018.08 but after the reboot processes all records went back to 27/08 again and also FW didn't update.
I am guessing there is a problem with the SD card but before I replace it wanted to ask if there is anything else I could try.

Thank you in advance
George


RE: Strange behavior LM5 Lite Power (FW 20170620) - admin - 31.08.2018

Make a backup and replace SD card, there's nothing else to try.