Logic machine as bacnet ms/tp slave - Printable Version +- Logic Machine Forum (https://forum.logicmachine.net) +-- Forum: LogicMachine eco-system (https://forum.logicmachine.net/forumdisplay.php?fid=1) +--- Forum: Gateway (https://forum.logicmachine.net/forumdisplay.php?fid=10) +--- Thread: Logic machine as bacnet ms/tp slave (/showthread.php?tid=2624) |
Logic machine as bacnet ms/tp slave - Carlos Padilla - 05.05.2020 Good companions, I hope you are excellent. I am writing to tell you if it is possible with the logic machine, read the variables of a meter that is Bacnet IP and pass it to Bacnet ms / tp through the RS485 ports it has. I have read in several threads that the logic machine does not accept Bacnet ms / tp, but maybe with the new firmware changes that have been made, it may be possible, so that's why I'm asking. Thank you and I will be attentive to your comments RE: Logic machine as bacnet ms/tp slave - Daniel - 05.05.2020 The only change in Bacnet were the bacnet units. Nothing new regarding MS/TP RE: Logic machine as bacnet ms/tp slave - Carlos Padilla - 05.05.2020 Ok. Thank you. |