Modbus 32-bit registers - MarcusH - 26.06.2020

Hi

I got an Eaton nzm-xmc-tc-mb, this unit got a 32-bit register with High byte and low byte. I've never worked with this before so im having probles understanding how it works.

I think I understand the logic, but I got no idea how I should pull the data and write it.

Register manual (PDF document):
https://www.google.com/url?sa=t&rct=j&q=&esrc=s&source=web&cd=&ved=2ahUKEwiG_9nlgp3qAhXuh4sKHaTZDLkQFjABegQIAxAB&url=ftp%3A%2F%2Fftp.moeller.net%2FDOCUMENTATION%2FAWB_MANUALS%2FMN01219001Z_EN.pdf&usg=AOvVaw1fqpTFseIkF9NK7jSPWqJn

Can someone explain how this works and maybe give me a starter script to get me going?

Best regards
Marcus H


RE: Modbus 32-bit registers - Daniel - 26.06.2020

Hi
Just try RTU read test with int32 and see what you get. In Modbus this is normal that you read several registers for single value.
BR


RE: Modbus 32-bit registers - admin - 26.06.2020

You should create a profile instead of using scripts. See this thread for some examples: https://forum.logicmachine.net/showthread.php?tid=839


RE: Modbus 32-bit registers - MarcusH - 26.06.2020

Hi,

Thanks Daniel, seems like i wasn't that far off after all. I keep getting this error, Resource temporarty unavailable. Is this an LM error or an device error?

I use script only when i want to read values for test, i find this much easier. When i get the values and understand the register i can, make my own register. Thanks for the link Smile


RE: Modbus 32-bit registers - Daniel - 26.06.2020

If you use RTU read test then you straight have all the parameters for profile, much simpler for me.