LM5 BTL Certified - Tokatubs - 30.10.2020

I have used LM5 as a bacnet gateway and have not had any issues. 

But now there are some text in a contract that i am wondering if the LM5 can do. Text is as follows: 

Device should support BACnet Standardized Device Profile (Annex L).
It should be used BIBB's standard for B-BC på BACnet IP, or B-AAC  or B-ASC on
BACnet MS/TP.
- BACnet units should be BTL-sertified. Should be documented with BACnet PICS, or a certicicat that confirms to BIBB`s.
-The unit should adoptble to exciting sites with changeble Bacnet device ID and UDP port.
-The unit should support BACnet encoding type ISO 10646 (UCS-2) / ANSI X3.4
(US-ASCII), that is changeble after installation. Equipment on BACnet IP should also suppport BBMD.


RE: LM5 BTL Certified - Daniel - 30.10.2020

If you need the cert itself you can use the SE version spaceLYnk. They certified the stack, We use exactly the same but no paper.
We don't support MS/TP


RE: LM5 BTL Certified - Tokatubs - 30.10.2020

I guess that it will never be asked about it. But then i know that it excist.
The rest is also ok, ?

It will be bacnet ip so lack of support for ms/tp is ok.


RE: LM5 BTL Certified - Daniel - 30.10.2020

Check yourself
https://www.bacnetinternational.net/catalog/manu/schneider%20electric/PICS_spaceLYnk_homeLYnk.pdf


RE: LM5 BTL Certified - Tokatubs - 30.10.2020

Perfect. 

Tried searching for it. But i was looking for the LM5. 

Thanks Daniel..