Logic Machine Forum
Limits on bacnet objects - Printable Version

+- Logic Machine Forum (https://forum.logicmachine.net)
+-- Forum: LogicMachine eco-system (https://forum.logicmachine.net/forumdisplay.php?fid=1)
+--- Forum: General (https://forum.logicmachine.net/forumdisplay.php?fid=2)
+--- Thread: Limits on bacnet objects (/showthread.php?tid=3848)



Limits on bacnet objects - Alberto.ricof - 02.02.2022

Good afternoon,

I am looking for information on the maximum number of objects that can be registered on an LM 5 Lite as an IP bacnet client?

I'm browsing through the manual and I can't find the data, maybe all the memory of the device is shared?

I am planning an application that requires several integrations with IP bacnet servers (1500 bacnet objects aprox.), and also a good part of KNX (about 120 knx devices approximately). I'm not sure whether to put 1 or 2 LM...

Thank you very much for your expert comments!

Greetings !!!


RE: Limits on bacnet objects - admin - 03.02.2022

The current BACnet client implementation is rather limited as everything has to be done via scripts and only a single script can handle all communication. If only reading BACnet devices is required then it can be done. If both reading and writing is needed I would not recommend more than 50-100 objects in total. There's also an app but it uses the same approach so the same limitations apply.
If LM is a BACnet server then it can handle 1500 objects.