Supervision - 2-byte unsigned integer Object - Fahd - 15.07.2022

Hi, 

I have a 2-byte unsigned integer object that I have mapped from an AHU that works with Modbus TCP/IP, 
However, the object works totally fine only from the object list I can send/read the value and the ahu communicate with that perfectly  BUT it's not the case from the supervision interface, 
I have created several icons  and each icon will send a value  0,1,2,3,4  
press icon 1 will send 0
press icon 2 it should send 1 but when I press it  sends 4 ! 
icon 3 work fine 
icon 4 work fine 
icon 5 works fine 
As you can see in the attachment the icon should send a fixed value "1"


RE: Supervision - 2-byte unsigned integer Object - admin - 15.07.2022

Maybe you have several icons on top of each other?


RE: Supervision - 2-byte unsigned integer Object - Fahd - 15.07.2022

(15.07.2022, 13:32)Fahd Wrote: Hi, 

I have a 2-byte unsigned integer object that I have mapped from an AHU that works with Modbus TCP/IP, 
However, the object works totally fine only from the object list I can send/read the value and the ahu communicate with that perfectly  BUT it's not the case from the supervision interface, 
I have created several icons  and each icon will send a value  0,1,2,3,4  
press icon 1 will send 0
press icon 2 it should send 1 but when I press it  sends 4 ! 
icon 3 work fine 
icon 4 work fine 
icon 5 works fine 
As you can see in the attachment the icon should send a fixed value "1"

I'm totally an idiot, I deleted that icon more than 5 times before posting in the forum and each time I do not click on save   At
Thank you.

Is there any limitation on the number of Modbus TCP/IP points that we could map?


RE: Supervision - 2-byte unsigned integer Object - Daniel - 15.07.2022

There is not really any limit but you have to take in to account the delay if more objects are added. It is single pooling queue for all TCP devices. For bigger registry amount it is recommended to use block read.


RE: Supervision - 2-byte unsigned integer Object - Fahd - 15.07.2022

(15.07.2022, 13:55)Daniel Wrote: There is not really any limit but you have to take in to account the delay if more objects are added. It is single pooling queue for all TCP devices. For bigger registry amount it is recommended to use block read.

There's 3 AHUs, and I will use 32 object from each one,
If you think that i will need to use block read, is there any script for that ?
Grateful for your replies


RE: Supervision - 2-byte unsigned integer Object - Daniel - 15.07.2022

Here is an example https://forum.logicmachine.net/showthread.php?tid=3375&pid=21834#pid21834
Usually this is used for bigger installations but it all depends how fast you need the values.
PS. Not every slave is supporting this.