Modbus communication error - Printable Version +- Logic Machine Forum (https://forum.logicmachine.net) +-- Forum: LogicMachine eco-system (https://forum.logicmachine.net/forumdisplay.php?fid=1) +--- Forum: Gateway (https://forum.logicmachine.net/forumdisplay.php?fid=10) +--- Thread: Modbus communication error (/showthread.php?tid=469) |
Modbus communication error - Mirco - 23.11.2016 Hi, is there a way to set an address group to 1 if there is an error with the modbus communication? I use the RTU Modbus communication with profiles. Thanks RE: Modbus communication error - admin - 23.11.2016 We have plans to add a status object, but it will work the other way round: 0 = missing, 1 = present/ok. As a work-around you can try monitoring one of the mapped objects last update time to check for failed communication. But this might not work if register value is not changing very often. RE: Modbus communication error - Mirco - 24.11.2016 Thanks! How can I check the last update time of an object with script or javascript? RE: Modbus communication error - admin - 24.11.2016 This is how you can delta time in seconds between now and last object update: Code: obj = grp.find('1/1/1') RE: Modbus communication error - Mirco - 24.11.2016 Thank you! RE: Modbus communication error - automatikas - 24.01.2017 missed the post. It does work fine. i used for loop as i have 36 devices Code: offline_time = 600 --offline detection time in seconds RE: Modbus communication error - Mirco - 18.05.2017 (23.11.2016, 08:01)admin Wrote: We have plans to add a status object, but it will work the other way round: 0 = missing, 1 = present/ok. As a work-around you can try monitoring one of the mapped objects last update time to check for failed communication. But this might not work if register value is not changing very often. Any news about the status object for modbus communication? RE: Modbus communication error - admin - 18.05.2017 Maybe for the next major version, not sure at the moment |