PowerTag Control I/O - Printable Version +- Logic Machine Forum (https://forum.logicmachine.net) +-- Forum: LogicMachine eco-system (https://forum.logicmachine.net/forumdisplay.php?fid=1) +--- Forum: Gateway (https://forum.logicmachine.net/forumdisplay.php?fid=10) +--- Thread: PowerTag Control I/O (/showthread.php?tid=5108) |
PowerTag Control I/O - FatMax - 23.11.2023 Has anyone had success controlling a PowerTag Control I/O relay through Modbus with a SL/W4K/LM? RE: PowerTag Control I/O - Daniel - 23.11.2023 Yes, I have Smartlink SI D for this. RE: PowerTag Control I/O - FatMax - 23.11.2023 Trying to do this through a Panel Server, but nothing happens when I send a 2 or 1 to register 37050.. I can read status and other objects just fine. Are you using the same registers for your setup? RE: PowerTag Control I/O - Daniel - 23.11.2023 Just this, provided by SE in SL RE: PowerTag Control I/O - FatMax - 23.11.2023 Ah, you are talking about a PowerTag energy meter. I have full control over those. I'm talking about this: https://www.se.com/au/en/product/A9XMC1D3/powertag-powertag-c-io-230v-digital-input-output-module/ RE: PowerTag Control I/O - Daniel - 23.11.2023 First time see this. RE: PowerTag Control I/O - domotiqa - 29.11.2023 but feedback is little disapointing on this product, it s mean to be for relay status only, i think I remember... work with si d (modbus ip), but with zibee direct I m not sure. Some people report to use some other brand mesh zigbee router (looks not working with the Zibee interface directly). But never try. RE: PowerTag Control I/O - FatMax - 29.11.2023 It was a stupid mistake, forgot to add writable = true to the profile. Works fine now! |