PowerTag Control I/O - FatMax - 23.11.2023

Has anyone had success controlling a PowerTag Control I/O relay through Modbus with a SL/W4K/LM?


RE: PowerTag Control I/O - Daniel - 23.11.2023

Yes, I have Smartlink SI D for this.


RE: PowerTag Control I/O - FatMax - 23.11.2023

Trying to do this through a Panel Server, but nothing happens when I send a 2 or 1 to register 37050..

I can read status and other objects just fine.

Are you using the same registers for your setup?


RE: PowerTag Control I/O - Daniel - 23.11.2023

Just this, provided by SE in SL


RE: PowerTag Control I/O - FatMax - 23.11.2023

Ah, you are talking about a PowerTag energy meter. I have full control over those. I'm talking about this:

https://www.se.com/au/en/product/A9XMC1D3/powertag-powertag-c-io-230v-digital-input-output-module/


RE: PowerTag Control I/O - Daniel - 23.11.2023

First time see this.


RE: PowerTag Control I/O - domotiqa - 29.11.2023

but feedback is little disapointing on this product, it s mean to be for relay status only, i think I remember...
work with si d (modbus ip), but with zibee direct I m not sure. Some people report to use some other brand mesh zigbee router (looks not working with the Zibee interface directly). But never try.


RE: PowerTag Control I/O - FatMax - 29.11.2023

It was a stupid mistake, forgot to add writable = true to the profile.

Works fine now!