This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

PowerTag Control I/O
#1
Has anyone had success controlling a PowerTag Control I/O relay through Modbus with a SL/W4K/LM?
Reply
#2
Yes, I have Smartlink SI D for this.
------------------------------
Ctrl+F5
Reply
#3
Trying to do this through a Panel Server, but nothing happens when I send a 2 or 1 to register 37050..

I can read status and other objects just fine.

Are you using the same registers for your setup?
Reply
#4
Just this, provided by SE in SL

Attached Files
.json   PowerTag.json (Size: 1.97 KB / Downloads: 5)
------------------------------
Ctrl+F5
Reply
#5
Ah, you are talking about a PowerTag energy meter. I have full control over those. I'm talking about this:

https://www.se.com/au/en/product/A9XMC1D...ut-module/
Reply
#6
First time see this.
------------------------------
Ctrl+F5
Reply
#7
but feedback is little disapointing on this product, it s mean to be for relay status only, i think I remember...
work with si d (modbus ip), but with zibee direct I m not sure. Some people report to use some other brand mesh zigbee router (looks not working with the Zibee interface directly). But never try.

Attached Files
.json   powerelay.json (Size: 695 bytes / Downloads: 5)
-----------
FRANCE SMARTHOME & SMARTBUILDING INTEGRATION
SE ECO EXPERT
Reply
#8
It was a stupid mistake, forgot to add writable = true to the profile.

Works fine now!
Reply