Error - Operation in progress - MODBUS TCP/IP - Fahd - 20.06.2024

Hi,

I received the attached error when I tried to use the read-test or using profiles

 Do you have any idea how to solve it?


RE: Error - Operation in progress - MODBUS TCP/IP - admin - 20.06.2024

Enable persistent connection mode in the device settings. This error is caused by the Modbus device supporting only a small number of open TCP connections. You can also try rebooting the Modbus device if the error persists.


RE: Error - Operation in progress - MODBUS TCP/IP - Fahd - 20.06.2024

(20.06.2024, 11:40)admin Wrote: Enable persistent connection mode in the device settings. This error is caused by the Modbus device supporting only a small number of open TCP connections. You can also try rebooting the Modbus device if the error persists.

I still have the same error (I rebooted the LM5),  I get the same error even when I try to read data from an invalid IP.

The communication was okay until the Modbus device went offline for 1 month.


RE: Error - Operation in progress - MODBUS TCP/IP - admin - 20.06.2024

Reboot the Modbus slave device. Rebooting LM won't solve this issue.


RE: Error - Operation in progress - MODBUS TCP/IP - Fahd - 20.06.2024

(20.06.2024, 11:52)admin Wrote: Reboot the Modbus slave device. Rebooting LM won't solve this issue.

Same


RE: Error - Operation in progress - MODBUS TCP/IP - Daniel - 20.06.2024

Then it seems your slave is broken