Error - Operation in progress - MODBUS TCP/IP - Printable Version +- Logic Machine Forum (https://forum.logicmachine.net) +-- Forum: LogicMachine eco-system (https://forum.logicmachine.net/forumdisplay.php?fid=1) +--- Forum: Gateway (https://forum.logicmachine.net/forumdisplay.php?fid=10) +--- Thread: Error - Operation in progress - MODBUS TCP/IP (/showthread.php?tid=5474) |
Error - Operation in progress - MODBUS TCP/IP - Fahd - 20.06.2024 Hi, I received the attached error when I tried to use the read-test or using profiles Do you have any idea how to solve it? RE: Error - Operation in progress - MODBUS TCP/IP - admin - 20.06.2024 Enable persistent connection mode in the device settings. This error is caused by the Modbus device supporting only a small number of open TCP connections. You can also try rebooting the Modbus device if the error persists. RE: Error - Operation in progress - MODBUS TCP/IP - Fahd - 20.06.2024 (20.06.2024, 11:40)admin Wrote: Enable persistent connection mode in the device settings. This error is caused by the Modbus device supporting only a small number of open TCP connections. You can also try rebooting the Modbus device if the error persists. I still have the same error (I rebooted the LM5), I get the same error even when I try to read data from an invalid IP. The communication was okay until the Modbus device went offline for 1 month. RE: Error - Operation in progress - MODBUS TCP/IP - admin - 20.06.2024 Reboot the Modbus slave device. Rebooting LM won't solve this issue. RE: Error - Operation in progress - MODBUS TCP/IP - Fahd - 20.06.2024 (20.06.2024, 11:52)admin Wrote: Reboot the Modbus slave device. Rebooting LM won't solve this issue. Same RE: Error - Operation in progress - MODBUS TCP/IP - Daniel - 20.06.2024 Then it seems your slave is broken |