Error - Operation in progress - MODBUS TCP/IP
I received the attached error when I tried to use the read-test or using profiles
 Do you have any idea how to solve it?
Enable persistent connection mode in the device settings. This error is caused by the Modbus device supporting only a small number of open TCP connections. You can also try rebooting the Modbus device if the error persists.
(20.06.2024, 11:40)admin Wrote: Enable persistent connection mode in the device settings. This error is caused by the Modbus device supporting only a small number of open TCP connections. You can also try rebooting the Modbus device if the error persists.
I still have the same error (I rebooted the LM5),  I get the same error even when I try to read data from an invalid IP.
The communication was okay until the Modbus device went offline for 1 month.
Reboot the Modbus slave device. Rebooting LM won't solve this issue.
(20.06.2024, 11:52)admin Wrote: Reboot the Modbus slave device. Rebooting LM won't solve this issue.
Same
Then it seems your slave is broken