Modbus Register Adresses 65-72 issue - Sam1 - 27.11.2025

Hello, 

I need and advice with modbus RS485 issue, 

Im not able to control addresses 65-72 through group objects, RX TX LED on Slave device flash only when I link our group object to the RTU adress, and it updates to correct value, so register is fine, I'm just not able to rewrite it - LM doesn't allow me to, it won't send anything to the RTU, adresses in Slave device are R/W, I have allowed this GO to write to the bus. 

Can we somehow allow Logic Machine to write values to these 7 adreses? RTU Device allows us to control these parameters from modbus. Do we need some kind of script for that? 

Thanks! 
BR


RE: Modbus Register Adresses 65-72 issue - admin - 27.11.2025

Post your device profile.


RE: Modbus Register Adresses 65-72 issue - Sam1 - 27.11.2025

File "List" is manufacturer adress list of Device 

Json is mine profile using in LM. 

Everything is working fine except for 65-72 adresses.


RE: Modbus Register Adresses 65-72 issue - admin - 27.11.2025

The correct field name is writable not writeable.
To avoid such errors use Modbus profiler app: https://forum.logicmachine.net/showthread.php?tid=5911


RE: Modbus Register Adresses 65-72 issue - Sam1 - 27.11.2025

... Thank You so much I haven't noticed this... Its okay

I'm so sorry x)