System messages - zoltan - 04.03.2017

I've got a few error logs on LM4 I dont like, can somebody explain them, please?

KNX/TP: Temperature warning

After this one I had a knx-deaf Homelynk once. This one is still talking on KNX, but Im not sure how long

KNX/TP: Transmitter error (send 0 receive 1)
KNX/TP: Protocol error (e.g. illegal control byte)

Just wonder what they are...


RE: System messages - Erwin van der Zwart - 04.03.2017

Hi Zoltan,

The issue you know was related to Siemens TPUART2 and we switched a long time ago to newer version TPUART and have never seen it again, so i don't think your LM controller will stop soon..

Temperature messages are send when exceeding a threshold, not sure but i believe 40 or 50 degrees, can it be the controller is inside a cabinet and temperature is that high inside cabinet?

The other 2 messages are new to me, can it be that you have set object to bit and send bytes to it from KNX side?

BR,

Erwin


RE: System messages - zoltan - 04.03.2017

Yes, it is inside cabinet, it is around 35, but I dont log it's temperature.

The other two appeared only once, maybe a month ago, but long after the site commissioning was done. Discovered it only now, because some strange behaviour was reported on the bus.

I have another issue, that I planned to address in different post, but I'll do it here now - every few days, maybe once a week I got a KNX disconnect/connect message in the log. Both in one second (same timestamp), or only one second apart.