Pause modbus function - Albertor - 26.06.2017

Good afternoon,

I'm looking at the forum how to pause the modbus function.
I have two devices configured through the .json mapping, however I have to punctually perform readings on the same devices manually, there are quite a few readings and here the errors begin ..

Is there any way to pause normal log reading, so I would pause while performing the manual reads, and at the end of the process I would revert to normal.

As always, many thanks in advance!
Best regards,
Alberto.


RE: Pause modbus function - admin - 26.06.2017

You should use modbus proxy functions so your script does not interfere with mapper readings: https://forum.logicmachine.net/showthread.php?tid=387&pid=1953#pid1953


RE: Pause modbus function - Albertor - 30.06.2017

(26.06.2017, 16:47)admin Wrote: You should use modbus proxy functions so your script does not interfere with mapper readings: https://forum.logicmachine.net/showthread.php?tid=387&pid=1953#pid1953

Thank you very much, works great!! Smile