Posts: 203
Threads: 46
Joined: Jul 2015
Reputation:
3
Hi,
I have an LM5 communicating with an arduino board via RS485 serial port.
It was working for several months but suddenly it stooped without any obvious reason.
Is there any easy way to check if there is a hardware problem with the RS485 port?
Thank you in advance
George
Posts: 8954
Threads: 48
Joined: Jun 2015
Reputation:
508
You can connect two RS485 ports on LM5 together and write a script to test communication between them.
Posts: 317
Threads: 42
Joined: Apr 2019
Reputation:
4
Hi. I have a problem every time I restart the LM. The rs485 port of the dali installation is not enabled, needing to re-enter the dali configuration and enable it.
I have another LM in another similar installation and it doesn't fail. I already updated the firm and the Dali package, and still doing the same. Can you think of it?
Thank you
Posts: 5855
Threads: 31
Joined: Aug 2017
Reputation:
266
Most likely your SD card is in read only mode and the configuration is not saved. Try changing any other configuration, reboot and see if it is still changed.
------------------------------
Ctrl+F5
Posts: 5855
Threads: 31
Joined: Aug 2017
Reputation:
266
Which FW?
------------------------------
Ctrl+F5
Posts: 5855
Threads: 31
Joined: Aug 2017
Reputation:
266
which port do you use?
------------------------------
Ctrl+F5
Posts: 8954
Threads: 48
Joined: Jun 2015
Reputation:
508
Can you post a screenshot of partitions table? System config > Status > System status > Partitions. You might have a device with separate flash storage for the database so object changes will be saved even when SD card is read-only.