I want to read the dutch smart meter, the p1 meter script is perfect for that.
but the only thing is the my LM is not near the smart meter.
I have a raspberry-pi next to the smartmeter with ser2net installed. how can I change this part of the script to use the ser2net?
Code: lastchar = '!'
require('serial')
port = serial.open('/dev/ttyUSB0', { -- Let op type van de slimme meter voor de onderstaande instellingen.
baudrate = 9600, --DSMR 2/3 = 9600 DSMR 4 = 115200
databits = 7, --DSMR 2/3 = 7 DSMR 4 = 8
stopbits = 1, --DSMR 2/3 = 1 DSMR 4 = 1
parity = 'even', --DSMR 2/3 = even DSMR 4 = none
duplex = 'full'
})
function readdata(port)
local char, buf
buf = {}
while true do
char = port:read(1)
-- error (timeout) or newline, stop
if char == nil or char == lastchar then
break
-- ignore cr char
elseif char ~= '\r' then
table.insert(buf, char)
end
end
return table.concat(buf)
end
data = readdata(port)
port:flush()
---------------------------------------------------------------
Thanks,
Mischa
Posts: 19
Threads: 6
Joined: Apr 2018
Reputation:
0
Figured out that it is not gonna work properly with ser2net to the LM
When starting a terminal, I get data but there is data missing. When starting terminal at the PI all data is present.
So ser2net would be fine for some commands, but i guess not for every second telegrams.
Mischa
Posts: 8905
Threads: 48
Joined: Jun 2015
Reputation:
508
I see no reason why it should not work. But since you already have pi there it might be easier to write a reader there and send parsed data to LM via http. Or use ser2net via tcp, there are many examples here on how to use tcp client.
Posts: 1820
Threads: 8
Joined: Jul 2015
Reputation:
121
Hi,
You could also use a Plugwise Smile P1 (aprox 90 euro) at the smart meter and read this device from LM over ethernet.
See https://openrb.com/read-plugwise-smile-p...-requests/
BR,
Erwin
Posts: 19
Threads: 6
Joined: Apr 2018
Reputation:
0
(03.05.2020, 09:24)Erwin van der Zwart Wrote: Hi,
You could also use a Plugwise Smile P1 (aprox 90 euro) at the smart meter and read this device from LM over ethernet.
See https://openrb.com/read-plugwise-smile-p...-requests/
BR,
Erwin
Hi Erwin,
Thanks going to take a look at that.
BR,
Mischa
Posts: 156
Threads: 31
Joined: Apr 2018
Reputation:
2
If i want to use the P1 meter script described in the first post. What port should be used? 232? and what is the max cable length?
Posts: 1820
Threads: 8
Joined: Jul 2015
Reputation:
121
13.01.2021, 09:33
(This post was last modified: 13.01.2021, 09:34 by Erwin van der Zwart.)
No you can't use RS232 direct as the signal of the P1 port is TTL so you need a TTL converter in any case, i always use (advise) this USB cable where the converter is build-in:
https://www.robbshop.nl/slimme-meter-kabel
Posts: 156
Threads: 31
Joined: Apr 2018
Reputation:
2
13.01.2021, 09:35
(This post was last modified: 13.01.2021, 09:36 by KoBra.)
ok thanks, the problem is the smart meter is around 100m from the logic machine, no wifi signal either. I have a spare cat6 connection there. Would it work if i hookup the P1 to the RJ45 cat 6, patch it to the outlet near the LM and than use this converter?
Posts: 1820
Threads: 8
Joined: Jul 2015
Reputation:
121
13.01.2021, 09:39
(This post was last modified: 13.01.2021, 09:39 by Erwin van der Zwart.)
No, that will never work over that distance as the P1 is a serial port, the only way to do this in your scenario is by using the Plugwise Smile P1 and conmnect it to the IP network with the spare cat6 cable you have.
Posts: 156
Threads: 31
Joined: Apr 2018
Reputation:
2
(13.01.2021, 09:39)Erwin van der Zwart Wrote: No, that will never work over that distance as the P1 is a serial port, the only way to do this in your scenario is by using the Plugwise Smile P1 and conmnect it to the IP network with the spare cat6 cable you have.
not a big fan of plugwise because i don't want to connect to their cloud. But Can i get all the data as the script is only fairly limited on the datapoints.
Posts: 1820
Threads: 8
Joined: Jul 2015
Reputation:
121
13.01.2021, 11:25
(This post was last modified: 13.01.2021, 11:27 by Erwin van der Zwart.)
This device can be used as a cloud solution but is not needed to config it like that, the device just reads the P1 data and exposes it as a .xml that can be read locally from the device..
The data is not limited by the plugwise, as this is a sample of the full DSMR data set:
Code: * string: /ISk5\2ME382-1003
0-0:96.1.1(4B413650303035313436373338393133)
1-0:1.8.1(11962.763*kWh)
1-0:1.8.2(11266.069*kWh)
1-0:2.8.1(00486.519*kWh)
1-0:2.8.2(01153.217*kWh)
0-0:96.14.0(0002)
1-0:1.7.0(0000.00*kW)
1-0:2.7.0(0000.05*kW)
0-0:17.0.0(0999.00*kW)
0-0:96.3.10(1)
0-0:96.13.1()
0-0:96.13.0()
Posts: 156
Threads: 31
Joined: Apr 2018
Reputation:
2
(13.01.2021, 11:25)Erwin van der Zwart Wrote: This device can be used as a cloud solution but is not needed to config it like that, the device just reads the P1 data and exposes it as a .xml that can be read locally from the device..
The data is not limited by the plugwise, as this is a sample of the full DSMR data set:
Code: * string: /ISk5\2ME382-1003
0-0:96.1.1(4B413650303035313436373338393133)
1-0:1.8.1(11962.763*kWh)
1-0:1.8.2(11266.069*kWh)
1-0:2.8.1(00486.519*kWh)
1-0:2.8.2(01153.217*kWh)
0-0:96.14.0(0002)
1-0:1.7.0(0000.00*kW)
1-0:2.7.0(0000.05*kW)
0-0:17.0.0(0999.00*kW)
0-0:96.3.10(1)
0-0:96.13.1()
0-0:96.13.0()
Tnx, i will take a look at it!
Posts: 156
Threads: 31
Joined: Apr 2018
Reputation:
2
(13.01.2021, 13:54)KoBra Wrote: (13.01.2021, 11:25)Erwin van der Zwart Wrote: This device can be used as a cloud solution but is not needed to config it like that, the device just reads the P1 data and exposes it as a .xml that can be read locally from the device..
The data is not limited by the plugwise, as this is a sample of the full DSMR data set:
Code: * string: /ISk5\2ME382-1003
0-0:96.1.1(4B413650303035313436373338393133)
1-0:1.8.1(11962.763*kWh)
1-0:1.8.2(11266.069*kWh)
1-0:2.8.1(00486.519*kWh)
1-0:2.8.2(01153.217*kWh)
0-0:96.14.0(0002)
1-0:1.7.0(0000.00*kW)
1-0:2.7.0(0000.05*kW)
0-0:17.0.0(0999.00*kW)
0-0:96.3.10(1)
0-0:96.13.1()
0-0:96.13.0()
Tnx, i will take a look at it! @Erwin,
2 questions:
- how do you take the XML to datapoints in Logic Machine
- do you know if it will work in the same way with the Smile P1 V3 that is launched?
Posts: 156
Threads: 31
Joined: Apr 2018
Reputation:
2
Finally i got it working for Plugwise Smile V3
Code: require('socket')
local mime = require('mime')
-- 1. CONFIGURATION: Mapping IDs to your Group Addresses
local mapping = {
-- Cumulative Totals (Wh -> kWh)
['986c55ddad604a018b5d216dc8aa37a1'] = { peak = '26/1/1', offpeak = '26/1/2' },
['f4fdea65cc874c5c8297193a6544dff0'] = { peak = '26/1/3', offpeak = '26/1/4' },
-- Instant Power Consumption (Watts)
['e90c4162ce094563bda979d3fe74eb58'] = '26/1/11', -- L1
['0ec9018894934dd6a4ef7e558838b844'] = '26/1/12', -- L2
['3fd23238e9e04dcc8fbf379ff9b24fc4'] = '26/1/13', -- L3
-- Instant Power Production (Watts)
['eb087cabceda45a9abb87103195e0049'] = '26/1/21', -- L1
['1f1a0baab8364a4f860084b075be4659'] = '26/1/22', -- L2
['4061da769ee8422c86e29634ed6f8a61'] = '26/1/23', -- L3
-- Voltages (Volts)
['a691532ba05442bc8d9fc0da21d1e674'] = '26/1/31', -- L1
['89a129b2e69945ee850b3e939235ed36'] = '26/1/32', -- L2
['fb657c3e3e3041d6b91e457781055c51'] = '26/1/33', -- L3
-- NEW: Current (Amperes)
['64c73a3ef3f04daf865e84d81168020c'] = '26/1/41', -- L1 Current
['b6bfa6f7685343da867a34dbd5e1bd03'] = '26/1/42', -- L2 Current
['4061da769ee8422c86e29634ed6f8a61'] = '26/1/43', -- L3 Current
}
-- 2. NETWORK SETTINGS
local ip = '192.168.1.1'
local auth = mime.b64('smile:********')
-- 3. FETCH DATA VIA TCP SOCKET
local client = socket.tcp()
client:settimeout(15)
local res, err = client:connect(ip, 80)
if res then
client:send("GET /core/domain_objects HTTP/1.1\r\n")
client:send("Host: " .. ip .. "\r\n")
client:send("Authorization: Basic " .. auth .. "\r\n")
client:send("Connection: close\r\n\r\n")
local response = {}
while true do
local chunk, status, partial = client:receive(2048)
local data = chunk or partial
if data then table.insert(response, data) end
if status == "closed" then break end
end
client:close()
local full_data = table.concat(response)
-- 4. PARSE AND WRITE
if #full_data > 1000 then
for log_id, content in full_data:gmatch('id=["\'](.-)["\'].->(.-)</%w+_log>') do
local target = mapping[log_id]
if target then
if type(target) == 'table' then
-- Dual Tariff Parsing
local offpeak = content:match('tariff=["\']nl_offpeak["\'].->(.-)</measurement>')
local peak = content:match('tariff=["\']nl_peak["\'].->(.-)</measurement>')
if offpeak then grp.checkupdate(target.offpeak, tonumber(offpeak) / 1000) end
if peak then grp.checkupdate(target.peak, tonumber(peak) / 1000) end
else
-- Single Measurement Parsing (Watts, Volts, Amps)
local val_str = content:match('<measurement.->(.-)</measurement>')
if val_str then
local n_val = tonumber(val_str)
grp.checkupdate(target, n_val)
-- log('Update ' .. target .. ' = ' .. n_val)
end
end
end
end
log('P1: Full Update Successful (' .. #full_data .. ' bytes)')
end
else
log('P1: Connection failed: ' .. tostring(err))
end
|