This forum uses cookies
This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus RTU - Relais-Board
#1
Hi

Would there be practical experiences available in relates to connecting and successfully controlling an

Eletechsup DC 12V 8 Ch RS485 Relay Board (Modbus RTU) ?


Kind regards,
Boris
Reply
#2
Do you have any documentation for it?
------------------------------
Ctrl+F5
Reply
#3
Hello Daniel

Thank you for your quick reply.

There are some rudimentary documentations available - although I was naively assuming, it would only require to set the ModBus-ID and ComPortSpeed in order to be discovered by the LM5. Have I been mistaken?


Kind regards, Boris 

.pdf   8 Channel RS485 Relay Manual.pdf (Size: 2.92 MB / Downloads: 99)
.pdf   8 channel rs485 commamd.pdf (Size: 233.49 KB / Downloads: 104)
Reply
#4
Connect it up and try reading from it via RTU read test. Use holding register and try address 0 and 1
------------------------------
Ctrl+F5
Reply