Modbus value_delta
We believe we have a problem related to the "value_delta" parameter when reading modbus registers.
Is this coefficient evaluated after the multiplication factor?
For example, if I read a power value in W and convert it to kW with a "value_multiplier" of 0.001, is the default/minimum factor 0.2 applied to the kW value? In this case the minimum value of 0.2 may be too large.
Delta check happens after all calculations are done. The difference between the current object value and the new value is checked.
Ok, but if I enter a "value_delta" value less than 0.2 in the modbus profile, which one will be used?
Thaks
Right now it cannot be set lower than 0.2. This will be changed in the next version. We'll publish an updated Modbus package once it's ready.
Install updated Package via System config-System-Package
https://dl.openrb.com/pkg/genohm-scada-m...1_imx6.ipk
https://dl.openrb.com/pkg/genohm-scada-m...1_imx6.sig
Clear browser cache after installation.