Posts: 5
Threads: 2
Joined: Feb 2025
Reputation:
0
I have a requirement to assign KNX group addresses to individual parameters on the Airconditioning widget
I can scroll and see on some of the fields the required group addresses, on other parameters (eg operation mode) I can not see any of the required group addresses
Why is this and how do I resolve?
Thanks
Posts: 5871
Threads: 35
Joined: Aug 2017
Reputation:
269
Widgets filter groups which have correct datatype for a particular object, it means you must convert it.
------------------------------
Ctrl+F5
Posts: 5
Threads: 2
Joined: Feb 2025
Reputation:
0
Thanks Daniel
2 questions.
Does Logic Machine automatically update datatypes from KNX if they are changed in ETS, or do i have to manually reimport
Is there a data dictionary of what datatype is valid for each field in a widget?
Thanks
Posts: 5871
Threads: 35
Joined: Aug 2017
Reputation:
269
1 no you should remove such group and import ets project or just change manually in object in LM.
2. Not really but you can ask which one you are not sure.
------------------------------
Ctrl+F5
Posts: 5
Threads: 2
Joined: Feb 2025
Reputation:
0
I've just reallocated the dpt types for HVAC Control mode 20.105 however it still doesnt show up as an object i can reference in Mosaic for the "climate mode status object"
Posts: 5871
Threads: 35
Joined: Aug 2017
Reputation:
269
------------------------------
Ctrl+F5