This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Connect N4AIA08 to LogicMachine
#1
I have a Modbus analog input device, which I would like to connect to my LogicMachine.

I managed to connect to that device with my laptop and read the inputs.
I also created the .json file, which I think it is correct.

Any help on how to connect to my LogicMachine and read the inputs?
Please keep in mind that this is the first time I work with Modbus,
so there are a lot I still need to learn.

Attached Files
.pdf   N4AIA08 N4AIB16 N4AIC24 Manual.pdf (Size: 619.72 KB / Downloads: 9)
.pdf   N4AIA08 N4AIB16 N4AIC24 MODBUS RTU Commamd.pdf (Size: 352.69 KB / Downloads: 4)
.json   N4AIA08 v20250327.json (Size: 1.37 KB / Downloads: 7)
Reply
#2
Connect it to LM, set RTU settings and then use Read test and check if you can read the values. Drop screenshot of correct configuration.
------------------------------
Ctrl+F5
Reply
#3
(28.03.2025, 08:28)Daniel Wrote: Connect it to LM, set RTU settings and then use Read test and check if you can read the values.  Drop screenshot of correct configuration.

I managed to make it work just fine. Thank you.