This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Acuvim energy meter
#1
Hi, 

I'm having som issues understadning if my configuration is correct for this meter:

https://www.accuenergy.com/support/modbu...dbus-map-3

I'm reading registers 16418-16419 with the use of the profile attached. How can I be sure that both registers are read other than adding datatype float32?


.json   LBC_AcuvimII.json (Size: 1.09 KB / Downloads: 5)
Reply
#2
This is how you define that LM will read both registers.
Correct this line
"value_multiplier\n\nvalue_multiplier\n\nvalue_multiplier\n\nvalue_multiplier": 0.001,
------------------------------
Ctrl+F5
Reply
#3
That messes up the kW conversion. The 0,001 should've taken care of that?

   
Reply
#4
Most likely you don't need multiplier at all. What value is returned when using Read test?
Reply
#5
At this very moment reading 16418 as float32 gives me 134130.4375 using read test.

This corresponds great with Value_multiplier in the profile set to 0,001 giving me 133,413 kW. So then I am sure that both registers are read, at least.
Reply
#6
What is the value on the meter itself?
------------------------------
Ctrl+F5
Reply
#7
It is at a remote location, so I don't have access to the meter display unfortunately.