Kamailio 3.3.7 on LM5M3: can the package be rebuilt? (branch limit 12, no dialog)
I am using the Kamailio SIP registrar described in
kb.logicmachine.net/integration/sip-server/ on an LM5M3. The device tree
reports "i.MX6UL LM5M3", ARMv7 Processor rev 5 (v7l), with genohm-scada
20251204. I installed it with the official resident-script method for the
i.MX6 target:
  - kamailio3 3.3.7-1_imx6, plus the maxfwd, usrloc, registrar, rr, sl
    and tm modules
  - your default kamailio.cfg, unmodified
First, it works well and I want to be clear about that. With no
configuration changes I get multiple contacts registered against a single
AoR, parallel forking to all of them, first-answer-wins with CANCEL to the
losing branches, and RTP flowing directly between the endpoints -
including between different subnets - since no media relay module is
loaded. This is exactly the behaviour I need from a registrar for
door-entry intercoms.
I have run into three limits that all appear to need a rebuild rather than
a configuration change, so my main question is simply: is a rebuilt
package for the i.MX6 target something that can be provided? If not, the
individual items below are moot.
1. BRANCH LIMIT OF 12
I registered 15 contacts against one AoR. All 15 registered successfully,
but an incoming call forked to only 12 of them. I repeated the test and
got 12 again, with a different subset of 12 each time. The log shows:
ERROR: <core> [dset.c:306]: append_branch(): max nr of branches exceeded
ERROR: registrar [lookup.c:298]: lookup(): failed to append a branch
Since this is MAX_BRANCHES in the core rather than a module parameter, I
cannot raise it from kamailio.cfg. I need at least 16 branches on a single
AoR.
Could the package be rebuilt with a larger MAX_BRANCHES, or with the limit
exposed as a core parameter?
2. DIALOG MODULE
It is not in the package. I looked for a kamailio3-mod-dialog .ipk at the
distribution path, using the same naming pattern as the six modules that
are published, and got 404. Same result for auth, auth_db, xlog, textops
and nathelper, while all six published modules return 200.
Without dialog there is nothing to clean up a session left behind when an
endpoint disappears without sending BYE. Device-side call timers cover
some of this, but not the case where only one side is gone.
Is adding this module possible?
3. AUTH / AUTH_DB
Also absent, so any device can register with any credentials. This is fine
on a test bench but not something I can leave in place.
4. KAMAILIO VERSION
3.3.7 is from 2013 and no longer receives security fixes. Is a current
branch (5.x or 6.x) for i.MX6 on the roadmap? I understand the
configuration syntax differs and that this is the largest of the four
requests.
ONE MORE THING THAT MADE DIAGNOSIS HARDER
There is no mi_fifo or kamctl, so I have no way to inspect the location
table and see which devices are currently registered. If there is another
way to read usrloc on the LM, I would be glad to hear it.
I am happy to test any package and report results back here. Smile
SIP server on LM is meant for very small use cases like door phone integration. We don't have plans to provide a newer package version as it is very rarely used.
You should install a separate device to handle SIP communication if you need a more complex configuration.