I've got a few error logs on LM4 I dont like, can somebody explain them, please?
KNX/TP: Temperature warning
After this one I had a knx-deaf Homelynk once. This one is still talking on KNX, but Im not sure how long
KNX/TP: Transmitter error (send 0 receive 1)
KNX/TP: Protocol error (e.g. illegal control byte)
Just wonder what they are...
Posts: 1772
Threads: 6
Joined: Jul 2015
Reputation:
118
04.03.2017, 10:59
(This post was last modified: 04.03.2017, 10:59 by Erwin van der Zwart.)
Hi Zoltan,
The issue you know was related to Siemens TPUART2 and we switched a long time ago to newer version TPUART and have never seen it again, so i don't think your LM controller will stop soon..
Temperature messages are send when exceeding a threshold, not sure but i believe 40 or 50 degrees, can it be the controller is inside a cabinet and temperature is that high inside cabinet?
The other 2 messages are new to me, can it be that you have set object to bit and send bytes to it from KNX side?
BR,
Erwin
Posts: 75
Threads: 17
Joined: Jan 2016
Reputation:
4
04.03.2017, 11:25
(This post was last modified: 04.03.2017, 11:27 by zoltan.)
Yes, it is inside cabinet, it is around 35, but I dont log it's temperature.
The other two appeared only once, maybe a month ago, but long after the site commissioning was done. Discovered it only now, because some strange behaviour was reported on the bus.
I have another issue, that I planned to address in different post, but I'll do it here now - every few days, maybe once a week I got a KNX disconnect/connect message in the log. Both in one second (same timestamp), or only one second apart.