01.07.2024, 09:01
Post what you have in System config > Status > System log.
|
problem with 4g modem
|
|
01.07.2024, 09:01
Post what you have in System config > Status > System log.
01.07.2024, 09:34
What LM hardware model are you using?
01.07.2024, 09:46
LM5p2-RIO3LTE
LM5M3CV15xA23010267
01.07.2024, 09:48
Do you have 3G/4G connection enabled? If it's disabled then the on-board modem won't be initialized.
01.07.2024, 10:19
It was disabled. When we try to enable it the LM stops responding.
01.07.2024, 10:22
This most likely caused by LM using mobile connection gateway instead of Ethernet.
Follow this guide if you only need SMS without 3G/4G: https://forum.logicmachine.net/showthrea...7#pid33127
01.07.2024, 12:05
It worked. Thanks!
I still have a strange situation. In the alert I still get "SMS handler lost connection" but the SMS are getting through. I only happens with a card from one provider. Using a card from a different provider it doesn't happen.
01.07.2024, 12:22
Modify AT:run() function in the user library as follows and post what you get in LM Logs tab.
Code: function AT:run()
01.07.2024, 14:08
Change the same function as follows and see if it helps.
Code: function AT:run() |
|