Modbus communication error
Exclamation
is there a way to set an address group to 1 if there is an error with the modbus communication?
I use the RTU Modbus communication with profiles.
We have plans to add a status object, but it will work the other way round: 0 = missing, 1 = present/ok. As a work-around you can try monitoring one of the mapped objects last update time to check for failed communication. But this might not work if register value is not changing very often.
Thanks!
How can I check the last update time of an object with script or javascript?
This is how you can delta time in seconds between now and last object update:
obj = grp.find('1/1/1') delta = os.time() - obj.updatetime log(delta)
Thank you! Big Grin
Thumbs Up
missed the post. It does work fine.
i used for loop as i have 36 devices
offline_time = 600 --offline detection time in seconds -- for i = START, STOP, STEP for i = 1, 36, 1 do  address = ('13/1/'..i)  obj = grp.find(address)  delta = os.time() - obj.updatetime  address = ('13/0/'..i)  if (delta > offline_time) then    grp.update(address, false)  else    grp.update(address, true)  end end
(23.11.2016, 08:01)admin Wrote: We have plans to add a status object, but it will work the other way round: 0 = missing, 1 = present/ok. As a work-around you can try monitoring one of the mapped objects last update time to check for failed communication. But this might not work if register value is not changing very often.
Any news about the status object for modbus communication?
Maybe for the next major version, not sure at the moment