23.11.2023, 08:12
Has anyone had success controlling a PowerTag Control I/O relay through Modbus with a SL/W4K/LM?
PowerTag Control I/O
|
23.11.2023, 08:12
Has anyone had success controlling a PowerTag Control I/O relay through Modbus with a SL/W4K/LM?
23.11.2023, 08:55
Trying to do this through a Panel Server, but nothing happens when I send a 2 or 1 to register 37050..
I can read status and other objects just fine. Are you using the same registers for your setup?
23.11.2023, 09:21
Ah, you are talking about a PowerTag energy meter. I have full control over those. I'm talking about this:
https://www.se.com/au/en/product/A9XMC1D...ut-module/
but feedback is little disapointing on this product, it s mean to be for relay status only, i think I remember...
work with si d (modbus ip), but with zibee direct I m not sure. Some people report to use some other brand mesh zigbee router (looks not working with the Zibee interface directly). But never try.
-----------
FRANCE SMARTHOME & SMARTBUILDING INTEGRATION SE ECO EXPERT
29.11.2023, 22:41
It was a stupid mistake, forgot to add writable = true to the profile.
Works fine now! |