27.03.2025, 09:13
Does LM support the Modbus function code 23 with profiles or with a script (luamodbus)?
Thanks.
Thanks.
Modbus function code 23 (#17)
|
27.03.2025, 09:13
Does LM support the Modbus function code 23 with profiles or with a script (luamodbus)?
Thanks.
27.03.2025, 09:18
See this: https://forum.logicmachine.net/showthrea...4#pid13244
Are you sure that function 23 is needed? Usually you can do writing and reading separately.
27.03.2025, 09:33
Thanks for the answer.
User manual of this device seems to require FC 23 as you can see in the picture. It's a Modbus interface for Mastervolt Battery charger (https://www.mastervolt.it/prodotti/maste...interface/)
28.03.2025, 11:13
When trying to implement communication with this device I always get the error "Bad file descriptor".
This LM uses both Modbus RTU ports with a different configuration. Code: require('luamodbus') This is the RTU port configuration:
28.03.2025, 11:14
RS must be uppercase in the port name.
I partially solved it using the send() function sending a string to the device.
In debug I can see the response which is complete and correct but the mb:receive() function returns a timeout error. Code: require('luamodbus') Logs report: Response error: Operation timed out Debug: * string: [01][17][00][00][00][06][00][00][00][06][0C][0A][01][AE][0F][00][00][00][11][00][00][00][00][91][AF] Waiting for a indication... <01><17><0C><0A><01><AE><0F><00><00><00><11><00><00><00><42><C1><35>ERROR Operation timed out: select The response captured by debug is complete and correct. I tried to change setreceivetimeout() and setresponsetimeout() with no effects.
Yesterday, 07:36
You can't use receive for master operation. The equivalent of your raw string using writereadregisters is this:
Code: mb:writereadregisters(0, 0x0A01, 0xAE0F, 0, 0x0011, 0, 0, 0, 6) |