CoolAutomation - CoolMasterNet integration
CoolMasterNet device uses TCP instead of RS-232 for communication, so we've updated the script to work with IP.
1. Create a resident script with 0 sleep interval, change 192.168.3.20 to CoolMasterNet device IP. Status information is polled every 3 seconds.
2. Create objects:
All objects must have VRV tag set.
Set object names, using the following scheme (full address and function):
L1.101 on/off - 1-bit, unit on/off control
L1.101 setpoint - unit setpoint, 2-byte floating point
L1.101 mode - unit mode, 1-byte (0 = cool, 1 = heat, 2 = fan, 3 = dry, 4 = auto)
L1.101 fspeed - fan speed, 1-byte (0 = low, 1 = medium, 2 = high, 3 = top, 4 = auto)
L1 on/off - 1-bit, on/off control for all units on a given line
L* on/off - 1-bit, on/off control for all units on all lines
You can create status objects by adding "status" to object name, example:
L1.101 on/off status
L1.101 setpoint status
L1.101 mode status
L1.101 fspeed status
L1.101 temp status - room temperature, 2-byte floating point
if not client then   require('socket')   require('genohm-scada.eibdgm')   IP = '192.168.3.20'   PORT = 10102   -- knx <> coolmaster mapping   knxtocm = {}   cmtoknx = {}   function reverse(src)     local res = {}     for k, v in ipairs(src) do       res[ v ] = k - 1     end     return res   end   -- integer<>text mode/fspeed value mapping   modetotext = { 'cool', 'heat', 'fan', 'dry', 'auto' }   texttomode = reverse(modetotext)   speedtotext = { 'low', 'med', 'high', 'top', 'auto' }   texttospeed = reverse(speedtotext)   -- get all tagged objects and set mapping   for _, object in ipairs(grp.tag('VRV')) do     local address, fn, stat = unpack(object.name:split(' '))     -- status object     if stat then       if not cmtoknx[ address ] then         cmtoknx[ address ] = {}       end       cmtoknx[ address ][ fn ] = {         id = object.id,         value = grp.getvalue(object.id),       }     -- control object     else       knxtocm[ object.id ] = {         address = address,         fn = fn,       }     end   end   function checkerror(res, err)     if not res then       sock:close()       sock = nil       alert('CoolMaster error: %s', tostring(err))     end     return res, err   end   function connect()     sock = socket.tcp()     sock:settimeout(5)     return checkerror(sock:connect(IP, PORT))   end   function send(data)     if not sock then       connect()     end     if sock then       checkerror(sock:send(data))     end   end   -- read single line from socket   function readline()     if not sock then       connect()     end     if sock then       return checkerror(sock:receive())     end   end   function updateknx(address, fn, value, datatype)     local object = cmtoknx[ address ] and cmtoknx[ address ][ fn ] or nil     -- object not found     if not object then       return     end     -- no value or same value, no update required     if value == nil or object.value == value then       return     end     -- save new value and write to knx     object.value = value     grp.write(object.id, value, datatype)   end   function parseline(line)     local address, status, setpoint, temp, speed, mode     line = line:gsub('>', '')     address = line:sub(1, 6)     -- address is invalid, cannot parse line     if address:sub(1, 1) ~= 'L' then       return     end     -- on/off status     status = line:sub(8, 9):lower() == 'on'     updateknx(address, 'on/off', status, dt.bool)     -- setpoint is integer     setpoint = line:sub(12, 13)     setpoint = tonumber(setpoint)     updateknx(address, 'setpoint', setpoint, dt.float16)     -- room temp is float, separated by comma     temp = line:sub(16, 17)     temp = tonumber(temp)     updateknx(address, 'temp', temp, dt.float16)     -- speed: low, med, high, auto     speed = line:sub(20, 23):lower():trim()     updateknx(address, 'fspeed', texttospeed[ speed ], dt.uint8)     -- mode: cool, heat, fan, dry, auto     mode = line:sub(25, 28):lower():trim()     updateknx(address, 'mode', texttomode[ mode ], dt.uint8)   end   -- read current status   function readstat()     send('ls\r\n')     -- read until error or end of stat     while true do       local line = readline()       -- timeout or end occured       if not line or line == 'OK' then         break       end       parseline(line)     end   end   -- handle group writes   function eventhandler(event)     local object, cmd, value, param     object = knxtocm[ event.dstraw ]     -- knx object not mapped, ignore     if not object then       return     end     -- on/off - boolean     if object.fn == 'on/off' then       value = knxdatatype.decode(event.datahex, dt.bool)       cmd = value and 'on' or 'off'     -- setpoint - floating point     elseif object.fn == 'setpoint' then       value = knxdatatype.decode(event.datahex, dt.float16)       param = string.format('%.1f', value)       cmd = 'temp'     -- mode (fan, dry, auto)     elseif object.fn == 'mode' then       value = knxdatatype.decode(event.datahex, dt.uint8)       cmd = modetotext[ value + 1 ]     -- speed (low, medium, high, auto)     elseif object.fn == 'fspeed' then       value = knxdatatype.decode(event.datahex, dt.uint8)       param = speedtotext[ value + 1 ]       if param then         cmd = 'fspeed'       end     end     -- got valid command     if cmd then       -- append address to command       cmd = cmd .. ' ' .. object.address       -- append additional parameter if set       if param then         cmd = cmd .. ' ' .. param       end       send(cmd .. '\r\n')       readline() -- command result     end   end   -- knx connection   client = eibdgm:new({ timeout = 1 })   client:sethandler('groupwrite', eventhandler)   -- start-up time   sec, usec = os.microtime() end -- handle knx client:step() -- read stats every 3 seconds diff = os.udifftime(sec, usec) if diff < 0 or diff >= 3 then   readstat()   sec, usec = os.microtime() end
Hello!
I need some assistance/direction with a Lua script, please.
I have installed a Clipsal 5500SHAC:
https://www.clipsal.com/products/detail?...cument-1=0
I have installed a CoolMasterNet to integrate with the Daikin VRV system. The CoolMasterNet has been configured and is working correctly. It is connected via IP.
https://coolautomation.com/news/c-bus-by...-hvac-vrf/
I need some assistance with the Lua script, please?
Thank you!
Torstein.
This script was created for LM,W4k,SL it will not work for NAC as they have different functions to write to objects. It require a bit of modifications.
in NAC Keywoards = TAG
(25.06.2020, 07:47)Daniel. Wrote: This script was created for LM,W4k,SL it will not work for NAC as they have different functions to write to objects.  It require a bit of modifications.
Thanks Daniel! Is there any way I can arrange for the required modifications to be done?
Thanks,
T.