Checksum XOR 4 bytes
Hello. Please tell me how you can summarize 4 bytes with the XOR operation. I have 5 bytes should have this amount
addr = {'0x01','0x03','0x05','0x07','0x09','0x0b','0x0d','0x0f','0x11','0x13','0x15','0x17','0x19','0x1b','0x1d','0x1f','0x21'} checksum = {'0xd3','0xd1','0xd7','0xd5','0xdb','0xd9','0xdf','0xdd','0xc3','0xc1','0xc7','0xc5','0xcb','0xc9','0xcf','0xcd','0xf3'} for i=1,17,1 do    command = string.char(0x04,0x04,addr[i],0xd2,checksum[i])    reply = writetoport(port, 0.2, command)    decoded = str2hex(reply)    log('Device address: eA'.. i-1 .. ', Result: ' .. decoded) end
I have 17 devices, 3 bytes is the address of the device, which changes, respectively, and the XOR checksum will also change
Use bit.bxor() and don't use quotes around numbers because not all functions will convert strings to numbers automatically.
function encode(...)   local checksum = bit.bxor(...)   return string.char(...) .. string.char(checksum) end addrs = {0x01,0x03,0x05,0x07,0x09,0x0b,0x0d,0x0f,0x11,0x13,0x15,0x17,0x19,0x1b,0x1d,0x1f,0x21} for _, addr in ipairs(addrs) do   command = encode(0x04,0x04,addr,0xd2)   reply = writetoport(port, 0.2, command)   decoded = str2hex(reply)   log('Device address: eA'.. i-1 .. ', Result: ' .. decoded) end
(21.12.2021, 13:49)admin Wrote: Use bit.bxor() and don't use quotes around numbers because not all functions will convert strings to numbers automatically.
Thanks for the help Smile
Please tell me more, how can I make a script that sends a request to rs232, after execution it starts up again, I tried to make a resident script with an interval of 0 so it does not have time to read data from the port
Can you describe your task in more detail? Protocol description would be helpful as well.
The main rule with serial ports is that only a single script can access the port. For reading you can set read length to -1 to skip waiting and read only the data that is already buffered by the driver.
(22.12.2021, 08:00)admin Wrote: Can you describe your task in more detail? Protocol description would be helpful as well.
Good afternoon. I need to constantly poll the room presence sensors through the rs232 port, on average, all sensors are polled once every 2.5 seconds. I transfer the result of the survey to group addresses. My script is hovering at the bottom
if not port then require('serial')     port, err = serial.open('/dev/RS232', {baudrate = 38400, databits = 8, stopbits = 1, parity = 'none', duplex = 'full'})     if port then     port:flush()   else     log('Error open port in: ' .. err)   end end function readline(port, timeout)   local char, buf   buf = {}   while true do     char = port:read(1, timeout or 0.2)     if char == nil or char == '\n' then       break      elseif char ~= '\r' then       table.insert(buf, char)     end   end   return table.concat(buf) end function writetoport(port, timeout, command)   port:write(command)   line = readline(port, timeout)   if #line > 0 then       return line   else     return "No reply received"   end end function str2hex(str)     raw_len = string.len(str)     i = 1       value = ''   while i <= raw_len do     if value then       if i == 4 then               value = string.byte(str, i)       end     else       value = string.byte(str, i)     end     i = i + 1   end   return value end function encode(...)   local checksum = bit.bxor(...)   return string.char(...) .. string.char(checksum) end addrs = {0x01,0x03,0x05,0x07,0x09,0x0b,0x0d,0x0f,0x11,0x13,0x15,0x17,0x19,0x1b,0x1d,0x1f,0x21,0x23} local sum = 0 for _, addr in ipairs(addrs) do   command = encode(0x04,0x04,addr,0xc8)   reply = writetoport(port, 0.1, command)   decoded = str2hex(reply)   if grp.getvalue('37/3/'.. sum)~=decoded then         grp.update('37/3/'.. sum, decoded)   end   sum = sum + 1 end value = event.getvalue() if value == true then     grp.update(event.dst, false) elseif value == false then     grp.update(event.dst, true) end
At the end, I check the state of the address where the script is and run it anew when the request is received.
This should be done via a resident script. Maybe add a small delay before each poll. You can also add port:flush() before writing and reading to clear the buffered data if there is anything left there.
(22.12.2021, 08:45)admin Wrote: This should be done via a resident script. Maybe add a small delay before each poll. You can also add port:flush() before writing and reading to clear the buffered data if there is anything left there.
I did thanks as advised, created a resident script with an interval of 3 seconds, and made the difference as a delay so that the script could finish the request, although I think I will remove the delay. The skrp is executed in an average of 2.5 seconds, and the difference in the interval of 3 seconds minus the query execution time will compensate for the pause after the execution of the script