25.07.2022, 14:41
Dears, i want a PID that calculates the supply water temp based on the setpoint and the actual temperature. But i have the PID script (see below) but i think the problem is i am keeping 0 is the fact that the output is in scale not temperature
-- clamp and set new output value
function PID2
etoutput()
local t, object, value, dt.scale
can somebody tell me how the datatype should be set to get the right output?
function PID2
PID22 = {
-- default params
defaults = {
-- invert algorithm, used for cooling
inverted = true,
-- minimum output value
min = 5,
-- maximum output value
max = 30,
-- proportional gain
kp = 0.1,
-- integral gain
ki = 0.1,
-- derivative gain
kd = 0.1,
-- PID2 init, returns new PID2 object
function PID2:init(params)
local n = setmetatable({}, { __index = PID2 })
local k, v
-- set user parameters
n.params = params
-- copy parameters that are set by user
for k, v in pairs(PID2.defaults) do
if n.params[ k ] == nil then
n.params[ k ] = v
-- reverse gains in inverted mode
if n.params.inverted then
n.params.kp = -n.params.kp
n.params.ki = -n.params.ki
n.params.kd = -n.params.kd
return n
-- resets algorithm on init or a switch back from manual mode
function PID2:reset()
-- previous value
self.previous = grp.getvalue(self.params.current)
-- reset iterm
self.iterm = 0
-- last running time
self.lasttime = os.time()
-- clamp iterm
self:clampiterm()
-- clamps iterm value
function PID2:clampiterm()
self.iterm = math.max(self.iterm, self.params.min)
self.iterm = math.min(self.iterm, self.params.max)
function PID2:setoutput()
self.output = math.max(self.output, self.params.min)
self.output = math.min(self.output, self.params.max)
value = math.floor(self.output)
local t = type(self.params.output)
-- write to output if object is set
if t == 'string' or t == 'table' then
if t == 'string' then
self.params.output = { self.params.output }
for _, output in ipairs(self.params.output) do
grp.write(output, value)
-- algorithm step, returns nil when disabled or no action is required, output value otherwise
function PID2:run()
local result
-- get manual mode status
local manual = self.params.manual and grp.getvalue(self.params.manual) or false
-- in manual mode, do nothing
if manual then
self.running = false
-- not in manual, check if reset is required after switching on
elseif not self.running then
self:reset()
self.running = true
-- compute new value if not in manual mode
if self.running then
-- get time between previous and current call
local now = os.time()
self.deltatime = now - self.lasttime
self.lasttime = now
-- run if previous call was at least 1 second ago
if self.deltatime > 0 then
result = self:compute()
return result
-- computes new output value
function PID2:compute()
local current, setpoint, deltasc, deltain, output
-- get input values
current = grp.getvalue(self.params.current)
setpoint = grp.getvalue(self.params.setpoint)
-- delta between setpoint and current
deltasc = setpoint - current
-- calculate new iterm
self.iterm = self.iterm + self.params.ki * self.deltatime * deltasc
self:clampiterm()
-- delta between current and previous value
deltain = current - self.previous
-- calculate output value
self.output = self.params.kp * deltasc + self.iterm
self.output = self.output - self.params.kd / self.deltatime * deltain
-- write to output
self:setoutput()
-- save previous value
self.previous = current
return self.output
