HTTP event from camera
Hi, i connect camera HTTP event to LM and i need to write group adress on the bus if event {alarm} is true.
this is log from LM
* table:
["alarm_2"]
  * bool: true
this is .lp script
require('apps')
vars = getvars()
log(vars)
Try this:
<? require('apps') vars = getvars() if vars.alarm_2 then   grp.write('1/1/1', true) end
(06.02.2023, 11:54)admin Wrote: Try this:
Thanks, what if alarm_2 wil be false?
Nothing will happen. It cannot be really false. It can be either nil, true or a string. You can add an else clause to write a different value to the object if needed.
(06.02.2023, 12:04)admin Wrote: Nothing will happen. It cannot be really false. It can be either nil, true or a string. You can add an else clause to write a different value to the object if needed.
Ok, this is works fine. I want to use scritp with 16 cam, each camera has diferent event name ( alarm_1, alarm_2, alarm_3,.....a, alarm_16) for log from witch is alarm send.
how to change script to works with this changing event name?
You can do it like this, alarm_1 will write to 1/1/1, alarm_2 to 1/1/2 and so on.
<? require('apps') vars = getvars() for i = 1, 16 do   if vars['alarm_' .. i] then     grp.write('1/1/' .. i, true)   end end
But you cannot use else clause here because it will reset all other alarms. Either the alarm variable should have some value (like 1/0) or you should check the IP address of the camera that sent this event.
(06.02.2023, 12:17)admin Wrote: You can do it like this, alarm_1 will write to 1/1/1, alarm_2 to 1/1/2 and so on.
ok, i thank for your help, only one adress i need to write, but log each of event, something like this:
<? require('apps') vars = getvars() for i = 1, 16 do   if vars['alarm_' .. i] then     grp.write('33/2/1', true)   end end log(vars)
it looks to work from each cam