This forum uses cookies
This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

integración modbus rtu con EASTRON SDM120
#1
hi,

I am new to this forum and I need your help to integrate an EASTRON SDM120 power meter with a spacelink (LSS100200). According to what has been said in the manuals I must create a profile with the data and variables modbus, which is realistic but it does not seem the only thing that needs to be done and that it did not obtain good results. I have read the forum and everything I need to create besides a profile "functions". I will appreciate if I can guide a little to know what I should do more clearly.

register Modbus  https://drive.google.com/a/kuniungen.com...sp=sharing

Then leave the profile you create.

{
"Product_code": "SDM120",
"Fabricante": "Eastron",
"Name": "SDM120",
"Product_range": "PM",
"Descripción": "SDM120 Medidor de energía",
"mapeo": [
{ "name": "Frecuencia", "bus_datatype": "float32", "tipo": "registrar", "dirección": 30000},
{ "name": "Voltaje", "bus_datatype": "float32", "tipo": "registrar", "dirección": 30071}
]
}



Regards

Attached Files
.pdf   SDM120-Modbus_protocol_V2.1.pdf (Size: 157.08 KB / Downloads: 20)
Reply
#2
Hi,

You can find all information you need to create the profiles in our application note AN027_SL.

See: http://www.schneider-electric.com/en/dow.../AN027_SL/

BR,

Erwin
Reply
#3
Key names like Product_code must be in lower case and keys values must be specified in English. Also, register addressing should start from 0: so Voltage address is 0, Frequency address is 70. There's Rtu read test option that you can use to quickly read any register/coil value without having to write a profile. Once you figure out the correct settings you can add them to your profile.
Some more info here: http://openrb.com/docs/modbus.htm
Reply
#4
(06.02.2017, 07:31)admin Wrote: Key names like Product_code must be in lower case and keys values must be specified in English. Also, register addressing should start from 0: so Voltage address is 0, Frequency address is 70. There's Rtu read test option that you can use to quickly read any register/coil value without having to write a profile. Once you figure out the correct settings you can add them to your profile.
Some more info here: http://openrb.com/docs/modbus.htm

Thanks for the help, you can already perform the complete reading of the meter, even if you have already done card readings of electric generators and other devices.

{"mapping":[
{"bus_datatype":14,"address":0,"type":"inputregister","units":" V","value_multiplier":1,"name":"volts","datatype":"float32"},
{"bus_datatype":14,"address":44,"type":"inputregister","units":" KVARH","value_multiplier":1,"name":"Total Reactive energy","datatype":"float32"}
],
"manufacturer":"EASTRON","name":"SDM120","product_range":"PM","description":"Powermeter SDM120"}


Big Grin Big Grin Big Grin
Reply
#5
Hi German, do you solve with SDM120CT?
Which is the right profile code?
I'm trying to use it but is not working for me.
Thanks
Reply
#6
(06.03.2024, 09:22)giolig Wrote: Hi German, do you solve with SDM120CT?
Which is the right profile code?
I'm trying to use it but is not working for me.
Thanks

Hola,

Si, me fue bien con la lectura, encontré un perfil que cree y lo pongo en adjunto, espero que te sirva.

Saludos.

Attached Files
.json   SDM120-EASTRON.json (Size: 1.88 KB / Downloads: 11)
Reply


Forum Jump: