Timer with manual stop
Hi.
I need help with a script for a lighting case, i have a spacelynk and Daligw, normal puschbutton to a binary input.
the costumer want to have 2 puschbuttons, 1st to start the light at 80% and after 60 min it will go down to 30 % in 10min and then 0%
the other button start at 80% for 240 min and then 30% in 10min and 0%.
It should be possible to turn off the light manually when the countdown has started, the binary input has 2 outgoing object for each channel (schneider).
Maybe stop/off with long press.
I have tried a Timer made here that`s seams to work, but if i send 0% to the gateway the script is still running and lights up when the lower value start.
The script i tested was this:
if not client then   timers = {     ['12/1/10'] = {       output = '12/1/12', -- dimmer control (0..100%)       onvaluehigh = 80, -- high output value in %       onvaluelow = 30, -- low output value in %       timeouthigh = 1 * 15, -- time to keep high value (in seconds)       timeoutlow = 1 * 10, -- time to keep low value (in seconds)     }   }   function timersetstate(timer, state)     grp.checkwrite(timer.output, timer['onvalue' .. state] or 0)     timer.state = state     timer.ticks = timer['timeout' .. state]   end   function timertimeout(timer)     local state = timer.state == 'high' and 'low' or 'off'     timersetstate(timer, state)   end   for _, timer in ipairs(timers) do     timer.state = 'off'   end   grp.sender = 'tm'   client = require('localbus').new(0.1)   client:sethandler('groupwrite', function(event)     local timer = timers[ event.dst ]     if timer and event.sender ~= grp.sender then       local value = tonumber(event.datahex, 16) or 0       if value == 1 then         timersetstate(timer, 'high')       end     end   end) end client:loop(1) for _, timer in pairs(timers) do   if timer.ticks then     timer.ticks = timer.ticks - 1     if timer.ticks == 0 then       timertimeout(timer)     end   end end
Try this modified script. It allows mapping one output to multiple inputs. When a timer is started all running timers for the same output are stopped. Writing to the output also stops any associated timers.
if not client then   timers = {     ['0/0/1'] = {       output = '0/0/255', -- dimmer control (0..100%)       onvaluehigh = 50, -- high output value in %       onvaluelow = 15, -- low output value in %       timeouthigh = 8, -- time to keep high value (in seconds)       timeoutlow = 3, -- time to keep low value (in seconds)     },     ['0/0/6'] = {       output = '0/0/255', -- dimmer control (0..100%)       onvaluehigh = 80, -- high output value in %       onvaluelow = 30, -- low output value in %       timeouthigh = 5, -- time to keep high value (in seconds)       timeoutlow = 2, -- time to keep low value (in seconds)     }   }   outputs = {}   function timerreset(addr)     for _, timer in pairs(timers) do       if timer.output == addr then         timer.ticks = nil         timer.state = 'off'       end     end   end   function timersetstate(timer, state)     grp.checkwrite(timer.output, timer['onvalue' .. state] or 0)     timer.state = state     timer.ticks = timer['timeout' .. state]   end   function timertimeout(timer)     local state = timer.state == 'high' and 'low' or 'off'     timersetstate(timer, state)   end   for _, timer in pairs(timers) do     timer.state = 'off'     outputs[ timer.output ] = true   end   grp.sender = 'tm'   client = require('localbus').new(0.1)   client:sethandler('groupwrite', function(event)     if event.sender == grp.sender then       return     end     local addr = event.dst     local timer = timers[ addr ]     if timer then       local value = tonumber(event.datahex, 16) or 0       if value == 1 then         timerreset(timer.output)         timersetstate(timer, 'high')       end     elseif outputs[ addr ] then       timerreset(addr)     end   end) end client:loop(1) for _, timer in pairs(timers) do   if timer.ticks then     timer.ticks = timer.ticks - 1     if timer.ticks == 0 then       timertimeout(timer)     end   end end
You are absolutely incredible, works immediately.
Thank you very much  Smile