Posts: 185
Threads: 38
Joined: Feb 2017
Reputation:
3
(17.06.2022, 13:23)admin Wrote: Not 120 but 127.0.0.1
You are right. The typo is only in the previous post, the address in the script is 127.0.0.1.
There are 10 kinds of people in the world; those who can read binary and those who don't
Posts: 8066
Threads: 43
Joined: Jun 2015
Reputation:
469
The error comes from having @ symbol in the password. It confuses the URL parser. Try using a password without @.
Posts: 185
Threads: 38
Joined: Feb 2017
Reputation:
3
(17.06.2022, 13:30)admin Wrote: The error comes from having @ symbol in the password. It confuses the URL parser. Try using a password without @.
Yes, I saw that as well, so I have changed the password so that there is no @ any more.
I now get "timeout" in stead of "host not found"
There are 10 kinds of people in the world; those who can read binary and those who don't
Posts: 8066
Threads: 43
Joined: Jun 2015
Reputation:
469
The IP blocker might have blocked local access because of wrong password. Reboot the device and try again.
Posts: 185
Threads: 38
Joined: Feb 2017
Reputation:
3
(17.06.2022, 13:34)admin Wrote: The IP blocker might have blocked local access because of wrong password. Reboot the device and try again.
I have also tried that. I actually down-powered it and repowered. Still same timeout.
There are 10 kinds of people in the world; those who can read binary and those who don't
Posts: 8066
Threads: 43
Joined: Jun 2015
Reputation:
469
What do you get logged from this script?
Code: require('socket.http')
log(socket.http.request('http://127.0.0.1/'))
Posts: 185
Threads: 38
Joined: Feb 2017
Reputation:
3
(17.06.2022, 14:15)admin Wrote: What do you get logged from this script?
Code: require('socket.http')
log(socket.http.request('http://127.0.0.1/'))
Here is the whole script:
Code: require('json')
require('socket.url')
require('socket.http')
user = 'admin'
Password = 'Ringshusveien_18'
tag = 'nyTrend'
-- parameters
daily = 365*24*60 -- 1 day
daily1year = 365*24*12 -- 365 day
daily2year = 2*365*24*12 -- 365 day
year5_d = 5*365 -- 5 year
obj = grp.tag(tag)
for _, addr in ipairs(obj) do
object = addr.address
alias = addr.name
trend = {
object = knxlib.encodega(object), -- object id in db
name = alias, -- trend name
type = trend_type,
resolution = 5, -- every 5 minute
precision = 2, -- floating point precision
count_resolution = 365*24*12, -- 1 year
count_daily = 5*365 -- 5 years
}
data = json.encode(trend)
post = 'data=' .. socket.url.escape(data)
grp.removetags(addr.name, tag)
res, err = socket.http.request('http://' .. user .. ':' .. password .. '@127.0.0.1/scada-main/trends/save', post)
log(res, err)
end
script.disable(_SCRIPTNAME)
I am basically logging the result and errors from the saving of the trend.
There are 10 kinds of people in the world; those who can read binary and those who don't
Posts: 8066
Threads: 43
Joined: Jun 2015
Reputation:
469
Works for me. Try running script from my previous post and see what you get in Logs.
Your script is also missing trend_type variable. It should be either 'C', 'D' or 'G' (counter, counter with negative delta or absolute value respectively).
Posts: 8
Threads: 0
Joined: Jun 2024
Reputation:
0
(19.02.2018, 15:39)Domoticatorino Wrote: (07.12.2016, 20:15)Pawel Wrote: Thanks Erwin, those scripts save me a lot of time. I made a small change and all objects with specific tag will have own trend:
Code: -- Batch adding trends - Created by Erwin van der Zwart - Schneider Electric Netherlands -----------
-- For spaceLYnk FW 1.2.1 or higher and homeLYnk FW 1.5.1 or higher --------------------------------
-- Refresh browser after creation to show the trends -----------------------------------------------
----------------------------------------- Start Parameters -----------------------------------------
-- Create trend to object with this tag
tag_name = "make_trend"
-- Set username and password for access to HL
username = 'admin'
password = 'admin'
-- Select trend type to create (or multiple types on same object)
create_trendtype_counter = true
create_trendtype_counter_with_negative_delta = true
create_trendtype_absolute_value = true
-- Set trend precicion (!Important! Can only be these values: 0 to 8)
trendprecision = 0
-- Set trend resolution (!Important! Can only be these values: 5 / 10 / 15 / 20 / 30 / 60 minutes))
trendresolution = 15
-- Set trend count resolution (!Important! Can only be these values: '30' = 30 days, '180' = 180 days, '365' = 1 year, '730' = 2 years, '1825' = 5 years
trendcountresolution = 365
-- Set trend count days (!Important! Can only be these values: '1' = 1 year / '2' = 2 years / '5' = 5 years / '10' = 10 years)
trendcountdaily = 10
-- Set show always 0 base line
trendshowzero = 0 -- 0 = disabled 1 = enabled
------------------------------------------ End Parameters ------------------------------------------
------------------------------ DON'T CHANGE ANYTHING UNDER THIS LINE -------------------------------
-- Load modules
require('json')
require('socket.url')
require('socket.http')
-- Set HL ip address as localhost
ip = '127.0.0.1'
-- Create url for trend creation
url = 'http://' .. username .. ':' .. password .. '@' .. ip .. '/scada-main/trends/save'
-- Function to send request to create trend
function url_send(trend_object, trend_name, trend_type, trend_resolution, trend_precision, trend_count_resolution, trend_count_daily, trend_show_zero, trend_id)
local trend = {
object = trend_object,
name = trend_name,
type = trend_type,
resolution = trend_resolution,
precision = trend_precision,
count_resolution = trend_count_resolution * 12 * 24, -- nr of days * nr of points in a hour at min resolution (60/5 = 12) * hours per day
count_daily = trend_count_daily * 365, -- nr of days * 365 days a year
show_zero = trend_show_zero,
id = trend_id,
}
data = json.encode(trend)
form_data = 'data=' .. socket.url.escape(data)
socket.http.TIMEOUT = 15
local res, code, response_header = socket.http.request(url, form_data)
return res, code, response_header
end
-- Set counters for creation log
number_of_trends = 0
number_failed = 0
objectwithtag = grp.tag(tag_name)
-- Loop for each group adress with specific tag
for key, value in pairs(objectwithtag) do
-- Get current group address from loop
current_GA = knxlib.decodega(value.id)
-- Get current object info
objectinfo = grp.find(current_GA)
-- Check if object excists
if objectinfo ~= nil then
-- Set parameters for request
trendobject = objectinfo.id
trendname = objectinfo.name
trendid = ''
-- Check if trend type 'Counter' should be created
if create_trendtype_counter == true then
-- Call function to send create request
result, code, response_header = url_send(trendobject, trendname, 'C', trendresolution, trendprecision, trendcountresolution, trendcountdaily, trendshowzero, trendid)
-- Calculate results for creation results log
if result == '{"success":true}' then
number_of_trends = number_of_trends + 1
else
number_failed = number_failed + 1
end
end
-- Check if trend type 'Counter with negative delta' should be created
if create_trendtype_counter_with_negative_delta == true then
-- Call function to send create request
result, code, response_header = url_send(trendobject, trendname, 'D', trendresolution, trendprecision, trendcountresolution, trendcountdaily, trendshowzero, trendid)
-- Calculate results for creation results log
if result == '{"success":true}' then
number_of_trends = number_of_trends + 1
else
number_failed = number_failed + 1
end
end
-- Check if trend type 'Absolute value' should be created
if create_trendtype_absolute_value == true then
-- Call function to send create request
result, code, response_header = url_send(trendobject, trendname, 'G', trendresolution, trendprecision, trendcountresolution, trendcountdaily, trendshowzero, trendid)
-- Calculate results for creation results log
if result == '{"success":true}' then
number_of_trends = number_of_trends + 1
else
number_failed = number_failed + 1
end
end
end
end
if number_failed == 0 then
log ("Created " .. number_of_trends .. " trends succesfully")
else
log ("Created " .. number_of_trends .. " trends succesfully and creation of " .. number_failed .. " trends failed")
end
-- Disable script when done automaticly
script.disable(_SCRIPTNAME)
Hi Pawel,
in this case don't you create .csv file?
Thanks.
Hello,
I have just carried out a test with this script which seems clear and complete to me. But it doesn't work for me?! I linked the Tag to three variables for the test and the log return is as follows: * string: Created 0 trends successfully and creation of 4 trends failed. Do you have any possible solutions?
Posts: 4930
Threads: 28
Joined: Aug 2017
Reputation:
225
Which controller and what firmware do you use?
------------------------------
Ctrl+F5
Posts: 8
Threads: 0
Joined: Jun 2024
Reputation:
0
(18.12.2024, 14:51)Daniel Wrote: Which controller and what firmware do you use?
Schneider LSS100200 (Spacelynk), firmware 3.0.0
Posts: 4930
Threads: 28
Joined: Aug 2017
Reputation:
225
Did you disable: Block unsafe functions in scripts: in general configuration?
------------------------------
Ctrl+F5
Posts: 8
Threads: 0
Joined: Jun 2024
Reputation:
0
(18.12.2024, 15:29)Daniel Wrote: Did you disable: Block unsafe functions in scripts: in general configuration?
I tried with and without the function, the result is the same.
Posts: 1793
Threads: 6
Joined: Jul 2015
Reputation:
120
19.12.2024, 14:57
(This post was last modified: 19.12.2024, 15:09 by Erwin van der Zwart.)
Can you try this version, it uses webrequests instead of URL with basic authentication that is not supported anymore in FW 3.0.0
Code: -- Batch adding trends v1.3 - Created by Erwin van der Zwart - Schneider Electric Netherlands -------------------
-- For spaceLYnk FW 3.0.0 or higher and Wiser for KNX FW 3.0.0 or higher ----------------------------------------
-- Make sure that "Block unsafe functions in scripts" is disbled in General Configuration
-- Refresh browser after creation to show the trends ------------------------------------------------------------
----------------------------------------------- Start Parameters ------------------------------------------------
-- Start address of objects
start_objectaddress = '3/0/0'
-- Trends for all objects between these range are created
-- End address of objects
end_objectaddress = '3/0/2'
-- Select trend type to create (or multiple types on same object)
create_trendtype_counter = false
create_trendtype_counter_with_negative_delta = false
create_trendtype_absolute_value = true
-- Select aggregate function (!Important! Can only be these values: AVERAGE / MIN / MAX / LAST))
trendaggregatefunction = 'AVERAGE'
-- Set trend resolution (!Important! Can only be these values: 5 / 10 / 15 / 20 / 30 / 60 minutes))
trendresolution = 5
-- Set trend precicion (!Important! Can only be these values: 0 to 8) decimal places
trendprecision = 2
-- Set trend count resolution (!Important! Can only be these values: '30' = 30 days, '180' = 180 days, '365' = 1 year, '730' = 2 years, '1825' = 5 years
trendcountresolution = 365
-- Set trend count days (!Important! Can only be these values: '1' = 1 year / '2' = 2 years / '5' = 5 years / '10' = 10 years)
trendcountdaily = 10
-- Set show always 0 base line
trendshowzero = 0 -- 0 = disabled 1 = enabled
------------------------------------------------ End Parameters -------------------------------------------------
------------------------------------ DON'T CHANGE ANYTHING UNDER THIS LINE --------------------------------------
-- Calculate start address to DB format
start_objectaddress = knxlib.encodega(start_objectaddress)
-- Calculate end address to DB format
end_objectaddress = knxlib.encodega(end_objectaddress)
-- Function to send request (in this case to create a trend)
function webrequest(mod, act, vars, data)
require('json')
require('dbenv')
local path
vars = vars or {}
function getvar(v)
return vars[ v ]
end
json.data = function()
return data or {}
end
if mod == 'plugin' then
path = 'plugins/' .. act .. '/web.lua'
else
path = 'web/' .. mod .. '/' .. act .. '.lua'
end
result = dofile('/lib/genohm-scada/' .. path)
-- Calculate results for creation results log
if result.success == true then
number_of_trends = number_of_trends + 1
else
number_failed = number_failed + 1
end
end
-- Function to create vars
function createvars(trend_object, trend_name, trend_type, trend_aggregate_function, trend_resolution, trend_precision, trend_count_resolution, trend_count_daily, trend_show_zero, trend_id)
local vars = {
object = trend_object,
name = trend_name,
type = trend_type,
aggregation = trend_aggregate_function,
resolution = trend_resolution,
precision = trend_precision,
count_resolution = trend_count_resolution * 12 * 24, -- nr of days * nr of points in a hour at min resolution (60/5 = 12) * hours per day
count_daily = trend_count_daily * 365, -- nr of days * 365 days a year
show_zero = trend_show_zero,
id = trend_id,
}
return vars
end
-- Set counters for creation log
number_of_trends = 0
number_failed = 0
-- Loop from startadres to end address to create trends
for i = start_objectaddress, end_objectaddress, 1 do
-- Get current group address from loop
current_GA = knxlib.decodega(i)
-- Get current object info
objectinfo = grp.find(current_GA)
-- Check if object excists
if objectinfo ~= nil then
-- Set parameters for request
trendobject = objectinfo.id
trendname = objectinfo.name
trendid = ''
-- Check if trend type 'Counter' should be created
if create_trendtype_counter == true then
-- Call function to create vars
requestdata = createvars(trendobject, trendname, 'C', trendaggregatefunction, trendresolution, trendprecision, trendcountresolution, trendcountdaily, trendshowzero, trendid)
webrequest('trends', 'save', {request = 'save'}, requestdata)
end
-- Check if trend type 'Counter with negative delta' should be created
if create_trendtype_counter_with_negative_delta == true then
-- Call function to send create vars
requestdata = createvars(trendobject, trendname, 'D', trendaggregatefunction, trendresolution, trendprecision, trendcountresolution, trendcountdaily, trendshowzero, trendid)
webrequest('trends', 'save', {request = 'save'}, requestdata)
end
-- Check if trend type 'Absolute value' should be created
if create_trendtype_absolute_value == true then
-- Call function to send create vars
requestdata = createvars(trendobject, trendname, 'G', trendaggregatefunction, trendresolution, trendprecision, trendcountresolution, trendcountdaily, trendshowzero, trendid)
webrequest('trends', 'save', {request = 'save'}, requestdata)
end
end
end
if number_failed == 0 then
log ("Created " .. number_of_trends .. " trends succesfully")
else
log ("Created " .. number_of_trends .. " trends succesfully and creation of " .. number_failed .. " trends failed")
end
-- Disable script when done automaticly
script.disable(_SCRIPTNAME)
Posts: 8
Threads: 0
Joined: Jun 2024
Reputation:
0
(19.12.2024, 14:57)Erwin van der Zwart Wrote: Can you try this version, it uses webrequests instead of URL with basic authentication that is not supported anymore in FW 3.0.0
Code: -- Batch adding trends v1.3 - Created by Erwin van der Zwart - Schneider Electric Netherlands -------------------
-- For spaceLYnk FW 3.0.0 or higher and Wiser for KNX FW 3.0.0 or higher ----------------------------------------
-- Make sure that "Block unsafe functions in scripts" is disbled in General Configuration
-- Refresh browser after creation to show the trends ------------------------------------------------------------
----------------------------------------------- Start Parameters ------------------------------------------------
-- Start address of objects
start_objectaddress = '3/0/0'
-- Trends for all objects between these range are created
-- End address of objects
end_objectaddress = '3/0/2'
-- Select trend type to create (or multiple types on same object)
create_trendtype_counter = false
create_trendtype_counter_with_negative_delta = false
create_trendtype_absolute_value = true
-- Select aggregate function (!Important! Can only be these values: AVERAGE / MIN / MAX / LAST))
trendaggregatefunction = 'AVERAGE'
-- Set trend resolution (!Important! Can only be these values: 5 / 10 / 15 / 20 / 30 / 60 minutes))
trendresolution = 5
-- Set trend precicion (!Important! Can only be these values: 0 to 8) decimal places
trendprecision = 2
-- Set trend count resolution (!Important! Can only be these values: '30' = 30 days, '180' = 180 days, '365' = 1 year, '730' = 2 years, '1825' = 5 years
trendcountresolution = 365
-- Set trend count days (!Important! Can only be these values: '1' = 1 year / '2' = 2 years / '5' = 5 years / '10' = 10 years)
trendcountdaily = 10
-- Set show always 0 base line
trendshowzero = 0 -- 0 = disabled 1 = enabled
------------------------------------------------ End Parameters -------------------------------------------------
------------------------------------ DON'T CHANGE ANYTHING UNDER THIS LINE --------------------------------------
-- Calculate start address to DB format
start_objectaddress = knxlib.encodega(start_objectaddress)
-- Calculate end address to DB format
end_objectaddress = knxlib.encodega(end_objectaddress)
-- Function to send request (in this case to create a trend)
function webrequest(mod, act, vars, data)
require('json')
require('dbenv')
local path
vars = vars or {}
function getvar(v)
return vars[ v ]
end
json.data = function()
return data or {}
end
if mod == 'plugin' then
path = 'plugins/' .. act .. '/web.lua'
else
path = 'web/' .. mod .. '/' .. act .. '.lua'
end
result = dofile('/lib/genohm-scada/' .. path)
-- Calculate results for creation results log
if result.success == true then
number_of_trends = number_of_trends + 1
else
number_failed = number_failed + 1
end
end
-- Function to create vars
function createvars(trend_object, trend_name, trend_type, trend_aggregate_function, trend_resolution, trend_precision, trend_count_resolution, trend_count_daily, trend_show_zero, trend_id)
local vars = {
object = trend_object,
name = trend_name,
type = trend_type,
aggregation = trend_aggregate_function,
resolution = trend_resolution,
precision = trend_precision,
count_resolution = trend_count_resolution * 12 * 24, -- nr of days * nr of points in a hour at min resolution (60/5 = 12) * hours per day
count_daily = trend_count_daily * 365, -- nr of days * 365 days a year
show_zero = trend_show_zero,
id = trend_id,
}
return vars
end
-- Set counters for creation log
number_of_trends = 0
number_failed = 0
-- Loop from startadres to end address to create trends
for i = start_objectaddress, end_objectaddress, 1 do
-- Get current group address from loop
current_GA = knxlib.decodega(i)
-- Get current object info
objectinfo = grp.find(current_GA)
-- Check if object excists
if objectinfo ~= nil then
-- Set parameters for request
trendobject = objectinfo.id
trendname = objectinfo.name
trendid = ''
-- Check if trend type 'Counter' should be created
if create_trendtype_counter == true then
-- Call function to create vars
requestdata = createvars(trendobject, trendname, 'C', trendaggregatefunction, trendresolution, trendprecision, trendcountresolution, trendcountdaily, trendshowzero, trendid)
webrequest('trends', 'save', {request = 'save'}, requestdata)
end
-- Check if trend type 'Counter with negative delta' should be created
if create_trendtype_counter_with_negative_delta == true then
-- Call function to send create vars
requestdata = createvars(trendobject, trendname, 'D', trendaggregatefunction, trendresolution, trendprecision, trendcountresolution, trendcountdaily, trendshowzero, trendid)
webrequest('trends', 'save', {request = 'save'}, requestdata)
end
-- Check if trend type 'Absolute value' should be created
if create_trendtype_absolute_value == true then
-- Call function to send create vars
requestdata = createvars(trendobject, trendname, 'G', trendaggregatefunction, trendresolution, trendprecision, trendcountresolution, trendcountdaily, trendshowzero, trendid)
webrequest('trends', 'save', {request = 'save'}, requestdata)
end
end
end
if number_failed == 0 then
log ("Created " .. number_of_trends .. " trends succesfully")
else
log ("Created " .. number_of_trends .. " trends succesfully and creation of " .. number_failed .. " trends failed")
end
-- Disable script when done automaticly
script.disable(_SCRIPTNAME)
It works perfectly! thank you very much for the time saved on creating the graphics
|