This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

VAV logic
#1
Hi. 
I need some help to make this script:
Fist i need a  ga/ input that chenges between summer and winter mode.
 
I have 4 g/a with cooling command 0-100%. 
I need to make a sum based on of the cooling modes are activ. The cooling is activ if the avlue is more than 0 (1-100)
This sum is the setpoint of the ventilation system that i need to send to on g/a

Summertime:
If not activ:                       
cooling cmd 1: 250
cooling cmd 2: 390
cooling cmd 3: 500
cooling cmd 4: 180
If activ:                       
cooling cmd 1: 250
cooling cmd 2: 650
cooling cmd 3: 850
cooling cmd 4: 250

Wintertime:
If not activ:                       
cooling cmd 1: 250
cooling cmd 2: 250
cooling cmd 3: 250
cooling cmd 4: 120
If activ:                       
cooling cmd 1: 250
cooling cmd 2: 250
cooling cmd 3: 250
cooling cmd 4: 120

I Also need a new g/a output ff the colling command is not 0 (1-100) to controll some vav dampers
 summer time i want the following:
cooling cmd 1: if 0 =0%, if 1-100 =100%
cooling cmd 2: if 0 =35%, if 1-100 =100%
cooling cmd 3: if 0 =42%, if 1-100 =100% 
cooling cmd 4: if 0 =46%, if 1-100 =100%
in  winter time i want the following:
cooling cmd 1: if 0 =0%, if 1-100 =0%
cooling cmd 2: if 0 =0%, if 1-100 =0%
cooling cmd 3: if 0 =0%, if 1-100 =0% 
cooling cmd 4: if 0 =0%, if 1-100 =0%
Reply
#2
Provide some examples how the final value is calculated. Two commands have the same output value for both active and inactive states.

To what value is 70% applied?
Reply
#3
I have 8 VAV dampers (2 per floor) that are controlled using a 0–100% command, corresponding to vMin–vMax.
Currently, some of the VAV dampers have the same vMin and vMax values, but this may change later.

When there is a cooling command, the corresponding VAV damper should switch to vMax = 100% in summer mode.
When this change to vMax occurs, I also need to increase the setpoint of the ventilation system accordingly.

Example – Setpoint Airflow Calculation:
Cooling Command Status Value
Cooling Cmd 1 Not active 250
Cooling Cmd 2 Active 650
Cooling Cmd 3 Active 850
Cooling Cmd 4 Not active 180

Resulting ventilation system setpoint = 1930

The 70% that i first decribe i see was wrong. I have change that part now i the main topic.
Reply