This forum uses cookies
This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus CRC?
#1
Hello,

I need a modbus CRC calculated in my script. Is there any way to use a built-in modbus function CRC generator trough a script? 

There is no sample script yet, I am in the planning phase still. Need to read a Merkurii 234 meter via rs485.
Reply
#2
Code:
1234567891011121314151617181920212223242526272829303132333435363738394041424344454647484950515253545556575859606162
function crc16modbus(msg)   local crctab, res, tmp   crctab = {     0x0000, 0xC0C1, 0xC181, 0x0140, 0xC301, 0x03C0, 0x0280, 0xC241,     0xC601, 0x06C0, 0x0780, 0xC741, 0x0500, 0xC5C1, 0xC481, 0x0440,     0xCC01, 0x0CC0, 0x0D80, 0xCD41, 0x0F00, 0xCFC1, 0xCE81, 0x0E40,     0x0A00, 0xCAC1, 0xCB81, 0x0B40, 0xC901, 0x09C0, 0x0880, 0xC841,     0xD801, 0x18C0, 0x1980, 0xD941, 0x1B00, 0xDBC1, 0xDA81, 0x1A40,     0x1E00, 0xDEC1, 0xDF81, 0x1F40, 0xDD01, 0x1DC0, 0x1C80, 0xDC41,     0x1400, 0xD4C1, 0xD581, 0x1540, 0xD701, 0x17C0, 0x1680, 0xD641,     0xD201, 0x12C0, 0x1380, 0xD341, 0x1100, 0xD1C1, 0xD081, 0x1040,     0xF001, 0x30C0, 0x3180, 0xF141, 0x3300, 0xF3C1, 0xF281, 0x3240,     0x3600, 0xF6C1, 0xF781, 0x3740, 0xF501, 0x35C0, 0x3480, 0xF441,     0x3C00, 0xFCC1, 0xFD81, 0x3D40, 0xFF01, 0x3FC0, 0x3E80, 0xFE41,     0xFA01, 0x3AC0, 0x3B80, 0xFB41, 0x3900, 0xF9C1, 0xF881, 0x3840,     0x2800, 0xE8C1, 0xE981, 0x2940, 0xEB01, 0x2BC0, 0x2A80, 0xEA41,     0xEE01, 0x2EC0, 0x2F80, 0xEF41, 0x2D00, 0xEDC1, 0xEC81, 0x2C40,     0xE401, 0x24C0, 0x2580, 0xE541, 0x2700, 0xE7C1, 0xE681, 0x2640,     0x2200, 0xE2C1, 0xE381, 0x2340, 0xE101, 0x21C0, 0x2080, 0xE041,     0xA001, 0x60C0, 0x6180, 0xA141, 0x6300, 0xA3C1, 0xA281, 0x6240,     0x6600, 0xA6C1, 0xA781, 0x6740, 0xA501, 0x65C0, 0x6480, 0xA441,     0x6C00, 0xACC1, 0xAD81, 0x6D40, 0xAF01, 0x6FC0, 0x6E80, 0xAE41,     0xAA01, 0x6AC0, 0x6B80, 0xAB41, 0x6900, 0xA9C1, 0xA881, 0x6840,     0x7800, 0xB8C1, 0xB981, 0x7940, 0xBB01, 0x7BC0, 0x7A80, 0xBA41,     0xBE01, 0x7EC0, 0x7F80, 0xBF41, 0x7D00, 0xBDC1, 0xBC81, 0x7C40,     0xB401, 0x74C0, 0x7580, 0xB541, 0x7700, 0xB7C1, 0xB681, 0x7640,     0x7200, 0xB2C1, 0xB381, 0x7340, 0xB101, 0x71C0, 0x7080, 0xB041,     0x5000, 0x90C1, 0x9181, 0x5140, 0x9301, 0x53C0, 0x5280, 0x9241,     0x9601, 0x56C0, 0x5780, 0x9741, 0x5500, 0x95C1, 0x9481, 0x5440,     0x9C01, 0x5CC0, 0x5D80, 0x9D41, 0x5F00, 0x9FC1, 0x9E81, 0x5E40,     0x5A00, 0x9AC1, 0x9B81, 0x5B40, 0x9901, 0x59C0, 0x5880, 0x9841,     0x8801, 0x48C0, 0x4980, 0x8941, 0x4B00, 0x8BC1, 0x8A81, 0x4A40,     0x4E00, 0x8EC1, 0x8F81, 0x4F40, 0x8D01, 0x4DC0, 0x4C80, 0x8C41,     0x4400, 0x84C1, 0x8581, 0x4540, 0x8701, 0x47C0, 0x4680, 0x8641,     0x8201, 0x42C0, 0x4380, 0x8341, 0x4100, 0x81C1, 0x8081, 0x4040   }   res = 0xFFFF   for i = 1, #msg do     tmp = msg:byte(i)     tmp = bit.bxor(tmp, res)     tmp = bit.band(tmp, 0xFF)     res = bit.rshift(res, 8)     res = bit.bxor(res, crctab[ tmp + 1 ])   end   return res end -- calcucate crc msg = '123456789' crc = crc16modbus(msg) -- split crc into 2 bytes byteh = bit.rshift(crc, 8) byteh = bit.band(byteh, 0xFF) bytel = bit.band(crc, 0xFF) -- append crc to message msg = msg .. string.char(byteh, bytel)
Reply
#3
Hello Admin,

I found this somewhere before, but I can't get it to work. The calculated CRC value is always something else than expected.

Here are few sample telegrams (last two bytes are the CRC):

02 08 05 [17 C3] - read address
02 00 02 [51 C1] - response

02 05 00 00 [11 9D] - read cumulative energy
02 03 00 D6 35 FF FF FF FF 00 00 BC 10 02 00 52 DE [78 B8] - response

This calculator gives a correct CRC for every check:
https://www.lammertbies.nl/comm/info/crc...ation.html

for the CRC-16 (Modbus) type.
Reply
#4
It does work, but the byte order is flipped. You just need to swap byteh and bytel when appending CRC to the source message.
Code:
1234567891011
msg = string.char(0x02, 0x03, 0x00, 0xD6, 0x35, 0xFF, 0xFF, 0xFF, 0xFF, 0x00, 0x00, 0xBC, 0x10, 0x02, 0x00, 0x52, 0xDE) crc = crc16modbus(msg) -- split crc into 2 bytes byteh = bit.rshift(crc, 8) byteh = bit.band(byteh, 0xFF) bytel = bit.band(crc, 0xFF) -- high=B8 low=78 alert(string.format('high=%02X low=%02X', byteh, bytel))
Reply
#5
It does work! ...and I need a sleep...

Thank you!
Reply