This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Carlo Gavazzi EM330
#1
I'm trying to implement an energy meter from Carlo Gavazzi EM 330, the registers I should read are 300041, but when I try with "read test" on the LM5, the highest register I can read is 65535.
Attached is the script I made and the modbus register for the meter.

Attached Files
.json   EM300.json (Size: 398 bytes / Downloads: 27)
.pdf   3-phase Modbus serial protocol EM and ET-rev.2.11.pdf (Size: 162.79 KB / Downloads: 39)
Reply
#2
Remove 3 from the beginning and subtract 1 so 300041 becomes 40 and so on.
Reply
#3
Thank you it worked perfectly
Reply
#4
Hi,

in attach my profile for EM-340 I am using. As I remember - they are totally the same, for my device I cannot change voltage and current transformation coefficient. Also exist models counting consumed and produced energy, I have only consumed power counting..

Profile is working except reactive power - should be checked..

Alex
.json   Gavazzi_EM340.json (Size: 6.96 KB / Downloads: 49)