25.07.2022, 14:41
Dears, i want a PID that calculates the supply water temp based on the setpoint and the actual temperature. But i have the PID script (see below) but i think the problem is i am keeping 0 is the fact that the output is in scale not temperature
-- clamp and set new output value
function PID2
etoutput()
local t, object, value, dt.scale
can somebody tell me how the datatype should be set to get the right output?
-- clamp and set new output value
function PID2

local t, object, value, dt.scale
can somebody tell me how the datatype should be set to get the right output?
Code:
123456789101112131415161718192021222324252627282930313233343536373839404142434445464748495051525354555657585960616263646566676869707172737475767778798081828384858687888990919293949596979899100101102103104105106107108109110111112113114115116117118119120121122123124125126127128129130131132133134135136137138139140141142143144145146
PID22 = {
-- default params
defaults = {
-- invert algorithm, used for cooling
inverted = true,
-- minimum output value
min = 5,
-- maximum output value
max = 30,
-- proportional gain
kp = 0.1,
-- integral gain
ki = 0.1,
-- derivative gain
kd = 0.1,
}
}
-- PID2 init, returns new PID2 object
function PID2:init(params)
local n = setmetatable({}, { __index = PID2 })
local k, v
-- set user parameters
n.params = params
-- copy parameters that are set by user
for k, v in pairs(PID2.defaults) do
if n.params[ k ] == nil then
n.params[ k ] = v
end
end
-- reverse gains in inverted mode
if n.params.inverted then
n.params.kp = -n.params.kp
n.params.ki = -n.params.ki
n.params.kd = -n.params.kd
end
return n
end
-- resets algorithm on init or a switch back from manual mode
function PID2:reset()
-- previous value
self.previous = grp.getvalue(self.params.current)
-- reset iterm
self.iterm = 0
-- last running time
self.lasttime = os.time()
-- clamp iterm
self:clampiterm()
end
-- clamps iterm value
function PID2:clampiterm()
self.iterm = math.max(self.iterm, self.params.min)
self.iterm = math.min(self.iterm, self.params.max)
end
-- clamp and set new output value
function PID2:setoutput()
local t, object, value, dt.scale
self.output = math.max(self.output, self.params.min)
self.output = math.min(self.output, self.params.max)
value = math.floor(self.output)
local t = type(self.params.output)
-- write to output if object is set
if t == 'string' or t == 'table' then
if t == 'string' then
self.params.output = { self.params.output }
end
for _, output in ipairs(self.params.output) do
grp.write(output, value)
end
end
end
-- algorithm step, returns nil when disabled or no action is required, output value otherwise
function PID2:run()
local result
-- get manual mode status
local manual = self.params.manual and grp.getvalue(self.params.manual) or false
-- in manual mode, do nothing
if manual then
self.running = false
-- not in manual, check if reset is required after switching on
elseif not self.running then
self:reset()
self.running = true
end
-- compute new value if not in manual mode
if self.running then
-- get time between previous and current call
local now = os.time()
self.deltatime = now - self.lasttime
self.lasttime = now
-- run if previous call was at least 1 second ago
if self.deltatime > 0 then
result = self:compute()
end
end
return result
end
-- computes new output value
function PID2:compute()
local current, setpoint, deltasc, deltain, output
-- get input values
current = grp.getvalue(self.params.current)
setpoint = grp.getvalue(self.params.setpoint)
-- delta between setpoint and current
deltasc = setpoint - current
-- calculate new iterm
self.iterm = self.iterm + self.params.ki * self.deltatime * deltasc
self:clampiterm()
-- delta between current and previous value
deltain = current - self.previous
-- calculate output value
self.output = self.params.kp * deltasc + self.iterm
self.output = self.output - self.params.kd / self.deltatime * deltain
-- write to output
self:setoutput()
-- save previous value
self.previous = current
return self.output
end