Object and Modbus Mapping Delete via Script
Hi all,
I need some help with database manipulation. I'm familiar with the correct methodology for adding objects via script.
What I am interested to know is the best practice for deleting objects via script.
Specifically, I need to delete an object and also remove the affiliated link in the modbus mapping.
EDIT: Also how to delete modbus devices via script.
I note the method does not work;
require('json')
function json.data()
return { id = 1 }
dofile('/lib/genohm-scada/web/modbus_devices/delete.lua')
Thanks in Advance,
BW
Try this:
addr = '1/1/1' -- delete object grp.delete(addr) -- clear modbus mapping id = buslib.encodega(addr) db:query('UPDATE modbus_mapping SET bus_address="" WHERE bus_address=?', id) -- restart modbus os.execute('sh /lib/genohm-scada/plugins/modbus/stop.sh; sleep 1; sh /lib/genohm-scada/plugins/modbus/start.sh')
Thanks! Works as expected.
Also, The following code worked to delete the entire modbus device. Care should be taken to remove the associated mapping in modbus_mapping as this will cause conflicts when adding new devices.
db:query('DELETE FROM modbus_devices', id)
Hello Admin,
Although I delete the object with the script, I can see it in the object list, so I still continue to see it in the modbus mapping table. how do I delete it from the scada object list (with script) what should I do,
Hi, you have to reload your browser (F5).
(22.02.2025, 23:13)isidur Wrote: Hello Admin,
yes it was fixed after reloading the page. thanks