Posts: 5658
Threads: 30
Joined: Aug 2017
Reputation:
252
You must select E - export flag for object to be updated on KNX side
------------------------------
Ctrl+F5
Posts: 312
Threads: 40
Joined: Apr 2019
Reputation:
4
Hi,
I have an installation with an LM5p2-KCD, and this is the second time the client has reported that the DALI lights have stopped working properly. The installation had been running without issues for almost a year, but these problems started about a month ago.
No modifications have been made to the installation since then. Is there any known issue currently with the DALI system? I mention this because on a previous occasion I had problems with the CANx-DALI gateways, and it was necessary to perform a hardware update.
The installation also includes a photovoltaic system, in case that could be related, as I’ve seen some colleagues experience issues with the KNX bus due to this.
It's worth mentioning that after restarting the LM, the system returns to normal operation. I don’t have a screenshot of the DALI monitor due to my oversight, but if I remember correctly, the message shown was:
Raw data: 80 | Information: Error: GW timeout
I would appreciate any guidance or information you can provide on this matter.
Best regards,
Posts: 5658
Threads: 30
Joined: Aug 2017
Reputation:
252
We would need to reproduce this bug, any hint on when this happen? What do you have on the bus? What is the voltage on dali?
------------------------------
Ctrl+F5
Posts: 8767
Threads: 48
Joined: Jun 2015
Reputation:
502
Can you provide remote access via ZeroTier?